Do you consider 40 cal/cm^2 as a firm cut off where no energized work can be performed?
Yes 43%  43%  [ 17 ]
No 35%  35%  [ 14 ]
Depends on the situation 23%  23%  [ 9 ]
Total votes : 40
Author Message
 Post subject: 40 cal/cm^2 Limit
PostPosted: Sun Nov 18, 2012 6:09 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1736
Location: Scottsdale, Arizona
This week's topic still stirs up a debate from time to time.

According the 2012 Edition of NFPA 130.7 (A) INFORMATIONAL NOTE NO. 3.

When incident energy exceeds 40 cal/cm^2 at the working distance, greater emphasis may be necessary with respect to de-energizing before working within the limited approach boundary of the exposed electrical conductors or circuit parts.

I highlighted "Informational Note" to emphasize this is technically not enforceable as requirements of the standards.

This week's question:
Do you consider 40 cal/cm^2 as a firm cut off where no energized work can be performed?
  • Yes
  • No
  • Depends on the situation

_________________
Jim Phillips, P.E.
Brainfiller.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Nov 19, 2012 4:56 am 
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 2178
Location: North Carolina
Can I vote twice? Technically no but without further guidance on arc blast and with this informational note hanging out there, it places everyone in a situation where it has to be treated as enforceable even when it is not. No guidance is given to "greater emphasis". I really dislike statements like that in Codes because they always result in going to the most conservative approach.

Some believe that this somewhat enforces equipment/task redesigns driving down the incident energy. The issue with this is that for instance if you have gear >15 kV, and you follow IEEE 1584 to the letter, this leaves you with using a theoretical calculation method which is grossly conservative, at 3X the actual tested values at 15 kV, and continues to become exponentially worse as voltage increases. Without a competing standard for >15 kV out there, the only other viable calculation method is ArcPro, which is widely recognized but closed source and does not have a shred of support in standards, journals, etc.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Nov 19, 2012 7:14 am 
Sparks Level

Joined: Wed Oct 29, 2008 6:06 am
Posts: 136
Location: Michigan
We require an EEWP for any task performed in areas exceeding 40 cal/cm^2 even if the task is something that is typically exempt from a permit such as voltage measurements (does not apply to verification of de-energization). We feel this allows these tasks to receive the greater emphasis suggested.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Nov 19, 2012 7:21 am 
Sparks Level

Joined: Tue Feb 24, 2009 7:05 am
Posts: 252
PaulEngr wrote:
Without a competing standard for >15 kV out there, the only other viable calculation method is ArcPro, which is widely recognized but closed source and does not have a shred of support in standards, journals, etc.

ArcPro is known to be the source behind the tables in the NESC. So there's at least a commonly used standard which supports it. Far from the same thing as a peer reviewed method, but more than nothing.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Nov 19, 2012 12:56 pm 

Joined: Sun Oct 05, 2008 5:00 pm
Posts: 17
I voted "depends on the situation". Performing actual live work, i.e. direct contact, exposure etc. - Not permitted. However, tasks such as operating equipment, opening closing breakers etc. i.e. "interaction" there often isn't much of a choice when you are trying to create an electrical safe work condition. (Although I'm sure Zog has a better method :) )


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Nov 19, 2012 2:43 pm 
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
I voted Yes beacuse as the one responsible for my field crews you have to draw the line somewhere, if it is >40cal find another way (Usuallly means get remote devices out there), if there is no other way then don't do it at all.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Jan 04, 2013 9:32 am 

Joined: Fri Feb 24, 2012 1:28 pm
Posts: 12
I vote yes but I wonder if it will ever become code. I imagine (based on my experience) there are many places out there that accept the dangers simply because it is not against code. While this practice is probably not in the companies best interests, it is still reasonable as a management view. "If it were that dangerous, the code would explicitly prohibit it." I would like to propose a question of the week of whether or not it should become code to prohibit live work over 40 cal. Obviously there would be a need for exceptions but it needs to start somewhere.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Jan 21, 2013 2:57 pm 
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 630
If you have a firm cutoff, you have a problem. It's not deenergized until it's tested, but you can't test because it's not yet deenergized. The only possible answer is no.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Jan 23, 2013 12:08 pm 
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
stevenal wrote:
If you have a firm cutoff, you have a problem. It's not deenergized until it's tested, but you can't test because it's not yet deenergized. The only possible answer is no.


Oh yeah, that elephant in the room, I change my answer to yes.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 9 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883