It is currently Sat Oct 24, 2026 12:42 am



Post new topic Reply to topic

Have you or someone you know used circuit tracers on 480V circuits?
Yes 45%  45%  [ 9 ]
No 55%  55%  [ 11 ]
Total votes : 20
Author Message
 Post subject: Use of Circuit Tracers
PostPosted: Sun Feb 17, 2013 3:05 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
I guess I'll take this week off. wbd asked a question this week so here it is:

In order to identify many circuits to develop or update a one line, one has to trace the conduit run to the end device starting at the breaker.

Have you or someone you know used circuit tracers on 480V circuits?
  • Yes
  • No

Your experiences are appreciated!

Thanks wbd!

If any of you have questions that you would like to see as part of the "Question of the Week", let me know and I'll post it here.

_________________
Jim Phillips, P.E.
Brainfiller.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Feb 18, 2013 7:27 am 
Sparks Level

Joined: Wed Jan 28, 2009 2:19 pm
Posts: 74
Location: Georgia
We occasionally use a circuit tracer as a last resort. First we verify the other circuits in the panel by tracing the conduit or de-energizing the circuit. We are left with the circuit that we cannot trace or de-energize. The untraced breaker will already be clearly labeled as to the equipment it feeds, then we use the circuit tracer to verify what we already know.

I would not use the circuit tracer for anything other than verifying what you already suspect to be true.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883