Maintaining Correct Working Distance
https://brainfiller.com/arcflashforum/viewtopic.php?f=33&t=2755
Page 1 of 1

Author:  Jim Phillips (brainfiller) [ Sun May 12, 2013 1:41 pm ]
Post subject:  Maintaining Correct Working Distance

The prospective incident energy used to define PPE requirements is based on the worker’s chest and head being a fixed distance away from the arc known as the working distance. Both NFPA 70E and IEEE 1584 reference this distance.

Here is this week’s question:

Do you (people you know) maintain the correct working distance when performing energized work?
  • Yes
  • No
  • We Try - not always possible
  • We don't perform energized work

Author:  Gary B [ Mon May 20, 2013 8:27 am ]
Post subject: 

It would seem the correct working distance is something the engineer chooses when performing a study and determining energy for PPE at that distance, and not something a tradesman has much discretion over. It is understood that if PPE is chosen for 18" distance and one's hands are closer than that; the protection may not be sufficient.

Author:  twm22 [ Wed May 29, 2013 5:40 pm ]
Post subject: 

Gary B wrote:
if PPE is chosen for 18" distance and one's hands are closer than that; the protection may not be sufficient.



I don't have the reference at hand, but I believe the working distance is for face/torso/neck.