 Post subject: Arc Flash and Current Limiting Fuses/Breakers
PostPosted: Sun May 19, 2013 11:40 am 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
Has your company or client added any current limiting fuses /circuit breakers as a result of an arc flash study?
  • Yes
  • No

_________________
Jim Phillips, P.E.
Brainfiller.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon May 20, 2013 7:11 am 
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 616
Location: Wisconsin
Yes and no.

It all depends on the situation.

If the arcing fault current is not sufficient to cause the fuse to enter its current limiting range, then we have gone so far as to recommend the fuse be replaced with a breaker. If the fault is sufficiently high then we evaluate the fuse in the the context of installed cost.

IMHO, generally it depends on the fuse curve, not whether it is current limiting or not.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon May 20, 2013 8:16 am 
Sparks Level

Joined: Wed Oct 29, 2008 6:06 am
Posts: 136
Location: Michigan
Added additional fuses, no. However, we've changed our stock inventory from RK5 to RK1 fuses. Where indicated by the arc flash hazard analysis we've replaced some of these older fused up in bus plugs to reduce the IE at the equipment panel on the floor.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon May 20, 2013 8:24 am 
Sparks Level

Joined: Thu Oct 18, 2007 7:10 pm
Posts: 262
Location: NW USA
No and yes: The question states "current limiting fuses" which is a specific category we have not installed as part of arc flash mitigation. We have; however, changed many fuse types and circuit breaker instantaneous settings to clear quickly on arcing fault current. So rather than limiting the current magnitude, we have limited it's duration.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883