Which disconnect switches should have an arc flash warning label?
Fusible disconnects 50 to 300 volts 25%  25%  [ 38 ]
Fusible disconnects 301 to 600 volts 29%  29%  [ 43 ]
Unfused disconnects 50 to 300 volts 17%  17%  [ 25 ]
Unfused disconnects 301 to 600 volts 23%  23%  [ 35 ]
It depends (please explain) 5%  5%  [ 8 ]
No labels necessary 1%  1%  [ 1 ]
Total votes : 150
Author Message
 Post subject: What equipment should have an arc flash warning label - Disconnect Switches
PostPosted: Sun Jul 28, 2013 3:24 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
There has been a great deal of discussion regarding what equipment should have an arc flash warning label. The 2012 Edition of NFPA 70E states:

[INDENT=1]Electrical equipment such as switchboards, panelboards, industrial control panels, meter socket enclosures and motor control centers that are likely to require examination, adjustment, servicing , or maintenance while energized...[/INDENT]

This is obviously not an all inclusive list and open to interpretation.

I have been asked by several people to explore this further using the Question of the Week. I don’t think this can be done with one question, so beginning this week, there will be a series of questions regarding equipment labeling.

Hopefully this will help provide guidance to those that are unsure about how far to carry the arc flash study / labeling. There has also been some good discussion elsewhere in this forum.

If you have a specific question you would like asked as part of this next series, please let me know.

Here is this weeks’ question - the first in a series.

Which disconnect switches should have an arc flash warning label?
  • Fusible disconnects 50 to 300 volts
  • Fusible disconnects 301 to 600 volts
  • Unfused disconnects 50 to 300 volts
  • Unfused disconnects 301 to 600 volts
  • It depends (please explain)
  • No labels necessary
SELECT ALL THAT APPLY

Your thoughts and comments are encouraged and welcome.

_________________
Jim Phillips, P.E.
Brainfiller.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Jul 29, 2013 6:31 am 
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 617
Location: Wisconsin
It is all about risk.
If the equipment will be opened, not just operated, the employee should be advised of any known hazards.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Jul 29, 2013 7:24 am 
Sparks Level
User avatar

Joined: Tue Apr 17, 2012 8:19 am
Posts: 253
Location: Charlotte, NC
It only makes sense to know where the disconnect is fed from, what upstream protective devices there are (if any), what the voltage to the disconnect is, and what the HRC is. It seems to be a logical extension of the list in NFPA 70E.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Jul 29, 2013 6:35 pm 
User avatar

Joined: Tue Apr 23, 2013 12:15 pm
Posts: 8
Location: Nashville, Tn
I`m very interested in everyone`s response to this question. I have been in the electrical trade for over 35 years and feel strongly that the potential arc flash hazards of a 30A/240V disc. would be so minimal that I feel like running a complete analysis on all of them in most facilities would be a waste of time and money. For example some of the small distribution facilities I`ve worked in it would mean doing a total analysis on 200-300 items instead of 40-50. In almost all situations the only thing you can do with a disc. live is check for the presence of voltage which would be covered under NFPA 70E table 130.7. Personally I feel that any disc. 100A or larger do have enough potential arc flash hazard to run a complete analysis on them. And I do think that all disc. should be marked as being a potential shock hazard but I`m leaning towards a somewhat generic label for all smaller disc. stating HRC 1 should be worn for voltage testing on 240V disc. and HRC 2 for 600V or less as per table 130.7.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Aug 01, 2013 2:32 pm 

Joined: Sat Nov 20, 2010 10:17 am
Posts: 13
Location: Victoria British Columbia
Table 130.7(c)(9) indicates a hazard risk category for each of these instances based on that one could simply label teh device with an HRC requirment equal to that in the table without the need for an extensive detailed analysis.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883