It is currently Fri Oct 30, 2026 5:01 pm
What is the condition of maintenance of your/your client’s electrical equipment?
Excellent - Better than most 2%  2%  [ 1 ]
Average - Pretty typical 53%  53%  [ 23 ]
Poor - What is maintenance? 30%  30%  [ 13 ]
Lots of clients / locations - we see it all 14%  14%  [ 6 ]
Total votes : 43
 Post subject: Condition of Maintenance - 2015 NFPA 70E
PostPosted: Sun Mar 02, 2014 10:40 am
The 2015 Edition of NFPA 70E is placing more emphasis on the condition of the electrical equipment and has the following language proposed:
110.1(B) The electrical safety program shall include elements that consider condition of maintenance of electrical equipment and systems.
Here is this week’s question:
  • Excellent - Better than most
  • Average - Pretty typical
  • Poor - What is maintenance?
  • Lots of clients / locations - we see it all
Jim Phillips, P.E.
Brainfiller.com
PostPosted: Tue Mar 04, 2014 9:57 am
Most of our customers and the equipment I see is maintained at the medium voltage and low voltage above 1,200amps fairly well. The lack of maintenance I see the most is in low voltage (208v&480v) panels where most of the work is done.
See attached picture. We are working to correct the multiple code violations in this imageand the many other violations discovered during the arc flash study.
PostPosted: Fri Mar 07, 2014 1:12 pm
I selected "average" but it is really hard to gauge just what average means. If most companies don't perform routine testing, does that become "average"?