Jeff S wrote:
I think there is too much shooting in the dark concerning this issue. In order to put this issue to rest, we need empirical evidence of what level of available short-circuit will be the threshold of an unsustainable arc at typical gap distances in 120/208V and 120/240V panelboards or 120V industrial control panels. Once we know that level of short-circuit, for equipment below that level of short-circuit, then all we have to do is determine the clearing time which one would guess at 1/2 cycle. Using that we most likely would be able to conclude those panels would be below the 1.2 cal/cm^2 level. For short-circuits above that sustainable level, then I think again empirical evidence will help. I would guess that the standard IEEE 1584 equations based on 3-phase short-circuits don't quite fit for single phase short-circuits.
IEEE 1584 testing has a single value at 208 V and I think 4 more at 250 V. All other test cases were so unstable that they didn't get any data. In DC testing tests have been conducted by Kinetrics at 130 V and they were able to get stable arcs at 5 kA and 20 kA at 0.5" spacing but any further and they could not get much of an arc. Even at 20 kA it self extinguished in 0.8 seconds. Most cases that have been published for even 208 or 240 VAC extinguish in about 1-2 cycles but there are some exceptions.
The real challenge though is that even while it is arcing the arc is so weak that it doesn't match the calculated arcing current to short circuit current ratio as calculated in IEEE 1584. And the arc can even extinguish and then reignite if it is 3 phase. Even with all this to consider though it would seem like we can simply do a lot of testing to measure the threshold below which arcs don't sustain and then use that as a lower cutoff for incident energy calculations. Not so! There are documented cases where the incident energy exceeds 1.2 cal/cm^2 and even a few lab cases where it got up over 4 cal/cm^2. This precludes any kind of "cutoff" approach. Like it or not, we're going to have to address this area. Hence the reason that I'm thinking that in the end it might have to be table driven.
Quote:
As for what I currently do: Apply the IEEE 1584 equations to the equipment as if it were 3 phase equipment and find the clearing time from the equipment TCC's. Obviously, 1584 says single-phase panels are outside of bounds for these equations, but what else is there? Declaring them to be of too low incident energy without empirical evidence is premature. Using this method, I quite often find 120/240V & 120/208V panels to have fairly high incident energies, quite often into Category 3. So if there is a general belief that this equipment would have a lower incident energy to warrant the PPE=0 category, the current IEEE 1584 equations don't support that contention. Clearly some additional guidelines are needed. Again, empirical evidence would be helpful.
NESC quotes empirical evidence and sets a threshold at 4 cal for 250 V or less regardless of the equipment configuraiton. Test work was performed by EPRI.