What data does the utility provide for arc flash studies (assuming data is provided)
Normal conditions 18%  18%  [ 18 ]
Maximum fault current 28%  28%  [ 28 ]
Minimum fault current (line out/contingency etc.) 15%  15%  [ 15 ]
Infinite bus 12%  12%  [ 12 ]
Not sure 0%  0%  [ 0 ]
Depends on the utility 28%  28%  [ 28 ]
Total votes : 101
Author Message
 Post subject: Electric Utility Data - Normal, Maximum, Minimum
PostPosted: Sun Nov 02, 2014 2:42 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
This week's QOW is a continuation of the subject about electric utility data.

What data does the utility provide for arc flash studies (assuming data is provided)

(Select all that apply)

Normal conditions
Maximum fault current
Minimum fault current (line out/contingency etc.)
Infinite bus
Not sure
Depends on the utility.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Electric Utility Data - Normal, Maximum, Minimum
PostPosted: Sun Nov 02, 2014 3:54 pm 
Plasma Level
User avatar

Joined: Wed May 07, 2008 5:00 pm
Posts: 881
Location: Rutland, VT
I choose Depends on Utility as I have seen all the choices from utilities.

_________________
Barry Donovan, P.E.
www.workplacesafetysolutions.com


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Electric Utility Data - Normal, Maximum, Minimum
PostPosted: Fri Nov 07, 2014 10:22 am 
Sparks Level
User avatar

Joined: Tue Oct 09, 2012 5:00 pm
Posts: 52
Most of the utilities that I deal with, provides maximum available fault current, although I specify to provide both Maximum & Minimum fault current in my RFI. So, I get back to them and dig the Minimum fault current and the range of their transformer impedance as well. This allows me to create multiple scenarios and analyze deeper.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Electric Utility Data - Normal, Maximum, Minimum
PostPosted: Wed Nov 12, 2014 7:08 am 

Joined: Mon Nov 04, 2013 2:36 pm
Posts: 4
Utilities are relunctan to provide this data. In the middle of the night after a storm, a line crew will replace fuses and transformers with what they have, and not with what it is supposed to be or was. One utility (name withheld) has stated they will base short-circuits on 1% transformer impedance, even though most transformers are 2% or higher. I saw a row of very old homes fed by a 350KVA transformer, The short circuit was well over the ratings of the usuall residental panelboards. Always request this data in Writing!!!


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883