Did you have any special requirement regarding the Prohibited Approach Boundary?
No 100%  100%  [ 33 ]
Yes (please elaborate) 0%  0%  [ 0 ]
Total votes : 33
Author Message
 Post subject: Previous Requirements for "Prohibited Approach Boundary"
PostPosted: Sun Nov 16, 2014 4:05 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
The 2015 edition of NFPA 70E has eliminated the Prohibited Approach Boundary (PAB). In part, because there wasn't any additional action required to be taken once you cross it.

Other than including the PAB on arc flash labels and referencing it in the electrical safety program as "the same as making contact with the electrical conductor"

Did you have any special requirement regarding the Prohibited Approach Boundary?

No
Yes (please elaborate)


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Previous Requirements for "Prohibited Approach Boundary"
PostPosted: Sun Nov 16, 2014 8:28 pm 

Joined: Mon Aug 11, 2008 5:00 pm
Posts: 31
I hadn't really thought about it that way but you are right. We only referenced it on labels and in the electrical safety practice as the same as making contact. That was it. I guess it makes sense to delete it. Except it will be on our labels for a while.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Previous Requirements for "Prohibited Approach Boundary"
PostPosted: Tue Nov 18, 2014 9:15 am 

Joined: Mon Nov 04, 2013 2:36 pm
Posts: 4
The prohibited approach boundary is the distance that untrained workers must be kept away from the live items to preventinadventant contact. Untrained workers should only be brought closer then this boundary with proper supervision. This was discussed at one NFPA class. Generally. when working with live equipment, warning tape [Danger Live Equipment - Do not Enter] and cones should be around the area to prevent bystanders and untrained people entering the area where they can contact live equipment.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Previous Requirements for "Prohibited Approach Boundary"
PostPosted: Wed Nov 19, 2014 11:31 am 
Sparks Level
User avatar

Joined: Tue Oct 09, 2012 5:00 pm
Posts: 52
I liked that 1 inch (Prohibited Approach Boundary) gone than Hazard Risk Category "0".


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Previous Requirements for "Prohibited Approach Boundary"
PostPosted: Wed Nov 19, 2014 3:54 pm 
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 619
Location: Wisconsin
JayWes wrote:
The prohibited approach boundary is the distance that untrained workers must be kept away from the live items to preventinadventant contact. Untrained workers should only be brought closer then this boundary with proper supervision. This was discussed at one NFPA class. Generally. when working with live equipment, warning tape [Danger Live Equipment - Do not Enter] and cones should be around the area to prevent bystanders and untrained people entering the area where they can contact live equipment.

You are describing the Arc Flash Boundary. You might want to check your notes.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Previous Requirements for "Prohibited Approach Boundary"
PostPosted: Mon Nov 24, 2014 5:17 am 
Sparks Level

Joined: Wed Oct 29, 2008 6:06 am
Posts: 136
Location: Michigan
This was a good change, because there wasn't any additional action required to be taken once crossed it was difficult to explain the significance of this boundary.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 6 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883