Which of the following are included in the study to account for poor device maintenance?
Legal Disclaimer 55%  55%  [ 30 ]
Device Testing and Maintenance 29%  29%  [ 16 ]
None of the Above/Something Else 16%  16%  [ 9 ]
Total votes : 55
Author Message
 Post subject: Arc Flash Study Legal Disclaimers, Testing, Device Condition
PostPosted: Sun Nov 30, 2014 3:06 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
The arc flash duration is normally determined from the protective device's time-current curves (TCC's). This approach assumes the device has been maintained and will operate according to the TCC. Most people realize this might be optimistic at best and therefore arc flash studies are usually accompanied by at least one of the following:

>A legal disclaimer stating that it is assumed the protective devices have been properly maintained and will operate according to their published TCC.

>Testing the protective devices and taking necessary corrective action

Here is this week's question:

Which of the following are included in the study to account for poor device maintenance?

(1) Legal disclaimer
(2) Device Testing and Maintenance
(3) None of the Above/Something Else

Select all that apply


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Study Legal Disclaimers, Testing, Device Condi
PostPosted: Mon Dec 01, 2014 7:27 am 
Sparks Level
User avatar

Joined: Tue Nov 12, 2013 6:31 am
Posts: 238
Location: Port Huron, Michigan
I did the study myself, and I'm also responsible for making sure maintenance gets done on the relevant equipment, so there aren't any disclaimers.

Jim Phillips (brainfiller) wrote:
The arc flash duration is normally determined from the protective device's time-current curves (TCC's). This approach assumes the device has been maintained and will operate according to the TCC. Most people realize this might be optimistic at best and therefore arc flash studies are usually accompanied by at least one of the following:

>A legal disclaimer stating that it is assumed the protective devices have been properly maintained and will operate according to their published TCC.

>Testing the protective devices and taking necessary corrective action

Here is this week's question:

Which of the following are included in the study to account for poor device maintenance?

(1) Legal disclaimer
(2) Device Testing and Maintenance
(3) None of the Above/Something Else

Select all that apply


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Study Legal Disclaimers, Testing, Device Condi
PostPosted: Tue Dec 02, 2014 7:58 am 

Joined: Mon Aug 11, 2008 5:00 pm
Posts: 31
Here is a question for a philosophical debate:

If a study has a disclaimer about the data, the condition of the equipment etc. and the utility usually has a disclaimer about their data being based on specific conditions that may change etc. then how much faith do we put into the results of an arc flash study?

It seems that many interpret a study as being an exact science when a) the calculations are approximate from what I understand and b) everything seems to have a disclaimer implying it might not be correct or could change.

This does not provide a comforting feeling when you view it this way.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Study Legal Disclaimers, Testing, Device Condi
PostPosted: Tue Dec 02, 2014 8:10 am 
Sparks Level
User avatar

Joined: Tue Nov 12, 2013 6:31 am
Posts: 238
Location: Port Huron, Michigan
L. Hankle wrote:
Here is a question for a philosophical debate:

If a study has a disclaimer about the data, the condition of the equipment etc. and the utility usually has a disclaimer about their data being based on specific conditions that may change etc. then how much faith do we put into the results of an arc flash study?

It seems that many interpret a study as being an exact science when a) the calculations are approximate from what I understand and b) everything seems to have a disclaimer implying it might not be correct or could change.

This does not provide a comforting feeling when you view it this way.


Not sure about others, but when I perform a study I consider a range of scenarios, to see how the incident energy values fluctuate, and generally use the highest values as the results of the study.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Study Legal Disclaimers, Testing, Device Condi
PostPosted: Tue Dec 09, 2014 2:03 pm 
Sparks Level

Joined: Thu Oct 18, 2007 7:10 pm
Posts: 262
Location: NW USA
even if everything works according to textbook, NFPA70E includes disclaimers that using the recommended methods will not eliminate injury. I quote those same disclaimers.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Study Legal Disclaimers, Testing, Device Condi
PostPosted: Mon Dec 15, 2014 8:50 am 

Joined: Fri Sep 10, 2010 7:48 pm
Posts: 17
Location: Idaho
There are many variables that are not accurately known when calculating the incident energy in an Arc Flash study and that is why we run multiple scenarios. From that we choose the worst case, erring on the side of caution. I think the biggest take aways from a properly executed Arc Flash study is the verification of the oneline, protective devices (fuse sizes, relay settings, etc.), coordination study, and equipment maintenance (operational checks, cleaning, adjustments, etc.). Arc Flash studies should bring an awareness of the system's state and provide information on areas of higher risk from which then can be prioritized to correct.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 6 posts ] 

All times are UTC - 7 hours