During your career, have you ever installed/removed a bus plug/tap while:
Energized WITHOUT PPE 38%  38%  [ 26 ]
Energized WITH PPE 24%  24%  [ 16 ]
De- energized/electrically safe 21%  21%  [ 14 ]
I have never done that type of work 18%  18%  [ 12 ]
Total votes : 68
Author Message
 Post subject: Install/Removing Bus Plugs/Taps
PostPosted: Sun Feb 15, 2015 2:53 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
This week's question is a continuation of the series about how work practices have evolved.

Many tasks that used to be considered routine and normal years ago are now rarely permitted.


During your career, have you ever installed/removed a bus plug/tap while:

Energized WITHOUT PPE
Energized WITH PPE
De- energized/electrically safe
I have never done that type of work


(you can select more than one answer)


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Install/Removing Bus Plugs/Taps
PostPosted: Mon Feb 16, 2015 6:42 am 

Joined: Mon Jun 09, 2014 9:19 am
Posts: 43
Several times in years past I have installed bus plugs while energized and no PPE. I have only seen one blow up from an arc flash event and thank goodness I wasn't the one holding it. As the tech was pushing the bus plug in he disrupted a lot of metal dust that had built up on the busway and the arc blew the bus plug back out and a 5ft fireball surrounded the busway. Our tech was in a scissor lift and was also caught in the flame but was not ignited since he had cotton clothing on. He did have some burnt hair though! After that happened we only installed plugs when we could get an outage since in the early and mid 90's we did not have any PPE.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Install/Removing Bus Plugs/Taps
PostPosted: Mon Feb 16, 2015 8:48 am 

Joined: Tue Apr 29, 2014 7:43 am
Posts: 18
Energized WITHOUT PPE
In about 1995 I was shown how to do this by an electrician. I have removed and installed 5 more since then, last one in 2006.
Some of these were done in a Square D QMB-4846 panel with QMB Saflex units. These were known to have switch handles which would fail, and you would not be sure whether they were turned off or not. There were replaced for this reason. Be very careful if you deal with these.
Since arc flash training has become more common and LOTO training improved, all have been done with power off. There were no incidents.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883