What percentage of equipment locations have a calculated incident energy above 40 cal/cm^2?
0 to 10 percent 65%  65%  [ 39 ]
11 to 20 percent 25%  25%  [ 15 ]
21 to 30 percent 3%  3%  [ 2 ]
above 30 percent (uh oh!) 7%  7%  [ 4 ]
Doesn't apply to me 0%  0%  [ 0 ]
Total votes : 60
Author Message
 Post subject: Percentage of Locations Above 40 cal/cm^2
PostPosted: Sun Mar 15, 2015 2:45 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1736
Location: Scottsdale, Arizona
This week's question is about the results of incident energy calculations exceeding the 40 cal/cm2 threshold that many use.

For most, the answer will be an approximation at best, especially if you are involved with arc flash studies at multiple facilities such as a consultant or corporate position.

The question refers to the value listed on the arc flash label and is used to define the arc flash protection requirements.

The question is:

On average, what percentage of equipment locations have a calculated incident energy above 40 cal/cm^2?

0 to 10 percent
11 to 20 percent
21 to 30 percent
above 30 percent :o
Doesn't apply to me


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Percentage of Locations Above 40 cal/cm^2
PostPosted: Sun Mar 15, 2015 6:16 pm 
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 2178
Location: North Carolina
I have about 2500 buses. Not practical to talk about "locations". About 25% are above "40 cal/cm^2" running the data raw out of SKM but this is not really accurate. Many of them are buses that are not accessible for work (so don't count) and many of them are where SKM defaults to Lee calculations because many of my busses are outside of 300-15 kV.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Percentage of Locations Above 40 cal/cm^2
PostPosted: Mon Mar 16, 2015 4:58 am 

Joined: Mon Jun 09, 2014 9:19 am
Posts: 43
We have between 30-40% of our locations across the system that have 40cal or higher energy. Our company has taken the stand that this is too high of a risk to our employees. We ar eworking on lowering those energies to 25cal or lower. with 138 stations across our system this is a huge task that involves many people.
Thanks!


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Percentage of Locations Above 40 cal/cm^2
PostPosted: Mon Mar 16, 2015 7:24 am 
Sparks Level

Joined: Fri Apr 15, 2011 7:43 am
Posts: 179
Location: Colorado
The question can be answered a couple of ways, either by the number of plants or the number of buses within a plant. We have hundreds of studies we have done but never kept statistical data, in general I would answer it this way:
approximately 75% of the plants we do studies for have 40cal+, of those somewhere between 5% and 15% of the buses are 40+.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Percentage of Locations Above 40 cal/cm^2
PostPosted: Mon Mar 16, 2015 7:37 am 
Sparks Level
User avatar

Joined: Tue Nov 12, 2013 6:31 am
Posts: 238
Location: Port Huron, Michigan
We were just talking about that this morning. I have exactly one switchgear breaker at 40 cal/cm2, and nothing higher.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Percentage of Locations Above 40 cal/cm^2
PostPosted: Mon Mar 23, 2015 7:00 am 
Sparks Level

Joined: Tue Jan 19, 2010 2:35 pm
Posts: 175
We've done studies in many locations and most of the larger facilities exceed 40 calories -at the Utility and at the meter and connected service. Once past that point, we rarely find locations exceeding 40 calories, that is unless it's a location with a large step down transformer with over current protection (on the secondary) that's very near or at the highest acceptable level. Even then, those rarely exceed 40 calories because of the 2 second rule.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Percentage of Locations Above 40 cal/cm^2
PostPosted: Thu Apr 02, 2015 1:26 pm 

Joined: Thu Apr 02, 2015 12:31 pm
Posts: 1
We ar eworking on lowering those energies to 25cal or lower. with 138 stations across our system this is a huge task that involves many people.
Thanks!

_________________
You can get score six sigma template


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 7 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883