It is currently Wed Oct 28, 2026 1:40 pm



Post new topic Reply to topic

Do you use the working distances from IEEE 1584:
Yes 58%  58%  [ 28 ]
No 8%  8%  [ 4 ]
Depends on the situation 29%  29%  [ 14 ]
Something else 4%  4%  [ 2 ]
Total votes : 48
Author Message
 Post subject: IEEE 1584 Working Distance
PostPosted: Sun Feb 21, 2016 12:29 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
A variation of this week's question was asked many years ago but study methods continue to evolve. IEEE 1584 - 2002 provides a table for suggested working distance to be used for the incident energy calculations. The distances are:

18 inches - Low Voltage MCCs and Panels
24 inches - Low Voltage Switchgear
36 inches - 5 kV and 15 kV Switchgear

Here is this week's question

Do you use the working distances from IEEE 1584:
Yes
No
Depends on the situation
Something else


Feel free to give us your thoughts about the working distance.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 1 post ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883