It has been a while since a question of the week was asked about the Arc Flash Boundary. This is the distance from a prospective arc flash where the incident energy is 1.2 cal/cm^2 which is the generally accepted value for the onset of a second degree burn. IEEE 1584 has a method for calculating this distance.

Since electrical safety practices continue to evolve, this week's question is about the Arc Flash Boundary. Although the AFB is required to be on the warning label and is a calculated value, many are opting to keep unprotected/unqualified workers further away from a possible arc flash during live work (which should be kept to a minimum). This week's question:

For your (client's) electrical safety practices, do you use:
Select up to 2 answers

Calculated AFB
Something larger (please explain)
Keep unprotected people out of the electrical room
It depends


Please feel free to elaborate


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Boundary - Calculated, Larger, Something Else?
PostPosted: Sat Jul 16, 2016 11:59 am 
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 2178
Location: North Carolina
I've had some buses where the "calculated" value is outright ridiculous...like hundreds of feet. Even if this was realistic, the building walls would come into play so at that point the building/room size matters, not the calculated number.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Boundary - Calculated, Larger, Something Else?
PostPosted: Sat Jul 16, 2016 12:59 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
PaulEngr wrote:
I've had some buses where the "calculated" value is outright ridiculous...like hundreds of feet. Even if this was realistic, the building walls would come into play so at that point the building/room size matters, not the calculated number.


Good point! I forgot about that case.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883