 Post subject: Largest Arc Flash Boundary
PostPosted: Sun Jul 23, 2017 12:54 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
Last week’s question was about large incident energy calculation and this week’s question parallels that theme.

It is about large calculated arc flash boundaries. Of course, actions such as using a 2 second cut off, adding arc energy reduction methods etc. can reduce the boundary but without those actions:

What is the largest calculated Arc Flash Boundary that you have seen?
Less than 10 feet (3 meters)
Between 10 feet (3 meters) and 30 feet (9 meters)
Greater than 30 feet (9 meters) – How large was it?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Largest Arc Flash Boundary
PostPosted: Mon Jul 24, 2017 1:33 pm 
User avatar

Joined: Wed Sep 12, 2012 9:13 am
Posts: 18
Location: Northern Colorado USA
Recently calculated a 19' boundary based on a 13.8kV/480V, 3PH, 800 kW transformer. Incident energy at the working standard distance for a panelboards was quite high and exceeded the 40 cal/cm2 limit. I did factor a 16' cable run and probably should increase that by quite a bit more. I am not certain how to calculate complex impedance for 3PH direct bury. Think you could do a blog post on that someday and include number of conductors for each phase?

~ Doug


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883