ekstra   ara
 Post subject: Infrared Inspection – Problems Found
PostPosted: Sun Feb 04, 2018 7:28 pm 
Offline
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1245
Location: Scottsdale, Arizona
This is a continuation of the series regarding infrared inspections.

The question is about problems found during the inspection.

If you have performed / had performed infrared scanning, what is the most common issue found?
Loose Connections
Faulty equipment
Overloads
Harmonics
Nothing - all is well
Other – please explain


Select all that apply


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Infrared Inspection – Problems Found
PostPosted: Mon Feb 05, 2018 9:31 am 
Offline

Joined: Thu Sep 04, 2014 1:37 pm
Posts: 1
infrared inspection problems: over tighten terminations, not so much loose terminations.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Infrared Inspection – Problems Found
PostPosted: Mon Feb 05, 2018 9:36 am 
Offline
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 442
I voted for loose connections, but the real problem is not usually that they are loose. Insufficient prep or wrong anti-oxidant used will cause them to go bad even when properly torqued..
Under the other category, include bad contact making on disconnects.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Infrared Inspection – Problems Found
PostPosted: Tue Feb 06, 2018 8:53 pm 
Offline
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 1878
Location: North Carolina
I often find loose stabs on large RK5 fuses. Not sure if that's loose connection or faulty equipment.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Infrared Inspection – Problems Found
PostPosted: Fri Feb 09, 2018 3:27 am 
Offline

Joined: Mon Feb 05, 2018 7:24 am
Posts: 1
We found motor contactor contacts fouling/pitted using infrared imaging.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Infrared Inspection – Problems Found
PostPosted: Mon Feb 12, 2018 5:45 pm 
Offline
Sparks Level

Joined: Tue Jan 19, 2010 2:35 pm
Posts: 96
Infrared is a great tool, provided you know what you're seeing. I got my certification back in 1985. That was when Infrared scanning was pretty new. Over the 35 + years I've done lots of IR scans. And the most common problem I've found was with disconnect switch contacts. Probably better than 90% of the problems were with disconnects. Of course, I wondered why? Aside from the manufacturing problems, I think the biggest cause for heating was (and is) people using disconnects to disconnect or connect an operating load. That may sound odd that disconnects are not supposed to be used to connect or disconnect operating loads, but that's not what their intended to do. They are supposed to disconnect and connect power; not disconnect and connect power to an operating load like a motor.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 6 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 3 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883