It is currently Thu Oct 22, 2026 2:42 am



Post new topic Reply to topic

What configuration/details would you likely use for the new arc flash model.
Keep it similar to what we have 17%  17%  [ 6 ]
Use whatever is most conservative 14%  14%  [ 5 ]
Use more specific/detailed data 34%  34%  [ 12 ]
Software defaults (if available) 11%  11%  [ 4 ]
Not sure 20%  20%  [ 7 ]
Doesn't apply - don't perform studies 3%  3%  [ 1 ]
Total votes : 35
Author Message
 Post subject: What configuration/details would you likely use for the new
PostPosted: Sat Oct 27, 2018 4:31 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
Many have purchased a copy of the last draft of IEEE 1584 and are studying it diligently prior to its publication.

One thing that is being discussed by many is the level of detail in the upcoming edition including adjustments for more exact enclosure sizes and different electrode configurations.

There are still configurations that are similar to the 2002 Edition of IEEE 1584 but there are many new ones as well.

Although a bit hypothetical until the new standard is out and implement in software, this week’s question - Without having performed a study yet based on the new edition of IEEE 1584:

What configuration/details would you likely use for the new arc flash model.

Keep it similar to what we have
Use whatever is most conservative
Use more specific/detailed data
Software defaults (if available)
Not sure
Doesn't apply - don't perform studies


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: What configuration/details would you likely use for the
PostPosted: Mon Oct 29, 2018 8:08 am 
Sparks Level
User avatar

Joined: Wed Jun 10, 2009 5:00 pm
Posts: 271
Location: Toronto
Shouldn't the options 1 and 2 be even considered since the old IEEE 1584 model has been superseded and it's not clear what is most conservative? Other than introducing enclosure dimensions, the new model doesn't require more information to perform the analysis (actually less information is required since grounding type was dropped and equipment class was traded for electrode configuration and enclosure size). Screenshots below show information required when using old IEEE 1584 year 2002 and new year 2018

Image
IEEE 1584 year 2002 based arc flash analysis inputs

Image
upcoming IEEE 1584 year 2018 based arc flash analysis inputs

_________________
Michael Furtak, C.E.T.
http://arcadvisor.com


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: What configuration/details would you likely use for the
PostPosted: Mon Oct 29, 2018 8:47 am 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
arcad wrote:
Shouldn't the options 1 and 2 be even considered since the old IEEE 1584 model has been superseded and it's not clear what is most conservative? Other than introducing enclosure dimensions, the new model doesn't require more information to perform the analysis (actually less information is required since grounding type was dropped and equipment class was traded for electrode configuration and enclosure size). Screenshots below show information required when using old IEEE 1584 year 2002 and new year 2018



The enclosure size can be modeled with more specific size detail - will people determine this since most don't determine the gap and use defaults. That is what some of this is about.

The electrode configuration can have an effect as well. 2002 used vertical electrodes and the next edition also has this option. However there are other options such as horizontal and vertical terminating into an insulating barrier. This is all a bit hypothetical at this point since the final edition standard has not been published yet and new software has not been released (that I know of) Just trying to gauge the feel of those that perform studies.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: What configuration/details would you likely use for the
PostPosted: Mon Oct 29, 2018 8:55 am 
Arc Level

Joined: Wed Jun 04, 2008 9:17 am
Posts: 428
Location: Spartanburg, South Carolina
If we have to include enclosure dimensions, it will vastly increase the time required for field work to perform a study. This will result in:
    1. Some other firm not including the required field time and our firm not getting the work.
    or
    2. Fewer customers performing studies because the cost is prohibitive


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: What configuration/details would you likely use for the
PostPosted: Mon Oct 29, 2018 9:31 am 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 499
jghrist wrote:
If we have to include enclosure dimensions, it will vastly increase the time required for field work to perform a study. This will result in:
    1. Some other firm not including the required field time and our firm not getting the work.
    or
    2. Fewer customers performing studies because the cost is prohibitive


+1.

_________________
Retired but I might visit once in awhile


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: What configuration/details would you likely use for the
PostPosted: Mon Oct 29, 2018 11:42 am 
Sparks Level
User avatar

Joined: Tue Oct 26, 2010 5:00 pm
Posts: 201
Location: Maple Valley, WA.
Unless the specifications for the AF study are very detailed and state what is required, I think that most consulting firms will use the most conservation (highest IE) electrode configurations and smallest box in the equipment. Most customers are not going to want to pay the extra costs to determine IE for each box within a piece of equipment (i.e MCC, Swtchboard, Switchgear).

_________________
Robert Fuhr, P.E.; P.Eng.
PowerStudies


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: What configuration/details would you likely use for the
PostPosted: Sun Nov 04, 2018 1:29 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
Robertefuhr wrote:
Unless the specifications for the AF study are very detailed and state what is required, I think that most consulting firms will use the most conservation (highest IE) electrode configurations and smallest box in the equipment. Most customers are not going to want to pay the extra costs to determine IE for each box within a piece of equipment (i.e MCC, Swtchboard, Switchgear).


Great comment - this is going to take some time to sort out!


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 7 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883