 Post subject: Device Setting Changes Found When Updating Arc Flash Study
PostPosted: Sun Dec 16, 2018 3:57 am 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
Arc Flash Studies have been around long enough that many are in their 2nd, 3rd updates/reviews.

This weeks question:

Have you found any changes to protective device settings since the last study was performed?

Yes - frequently
Yes - a few times
No - same settings as before
Havn’t revised study yet
Not applicable.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Device Setting Changes Found When Updating Arc Flash Stu
PostPosted: Sun Dec 16, 2018 9:17 am 
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 616
Location: Wisconsin
I have found a few at some customers.

Many of the changes appeared to have happened during breaker testing as opposed to being an intentional act.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Device Setting Changes Found When Updating Arc Flash Stu
PostPosted: Sun Dec 16, 2018 11:13 am 
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 2178
Location: North Carolina
Oh you mean where field changes were made. Mostly I've just found errors by the engineering firm.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Device Setting Changes Found When Updating Arc Flash Stu
PostPosted: Tue Dec 18, 2018 7:44 pm 

Joined: Fri Sep 10, 2010 7:48 pm
Posts: 17
Location: Idaho
Most of the settings I have had to change were due to improper coordination. It appears previous AF studies were based on solely on providing labels.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Device Setting Changes Found When Updating Arc Flash Stu
PostPosted: Wed Jan 02, 2019 11:00 pm 

Joined: Wed Jan 02, 2019 10:20 pm
Posts: 1
I have frequently encountered breaker settings that needed to be changed, for several reasons that are part of the nature of my employer's business (data centers). We have legacy buildings that weren't necessarily well-coordinated in the first place, inconsistencies in settings for similar equipment in the same building due to different engineers working on different construction phases, field changes during commissioning that weren't adjusted to the recommended settings... even studies with equipment that is missing altogether because we used to have a construction team in-house, who added panels as needed without making sure they were added to the study. Since our data centers are expanding quickly it seems like I always have an arc flash study to review and mark up with all of these corrections.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883