| Author |
Message |
|
timandjen94
|
Post subject: extraction time in arc flash studies Posted: Wed May 01, 2019 12:52 pm |
|
Joined: Wed May 01, 2019 12:47 pm Posts: 1
|
|
I am interested to know if there is a standard amount of time to use for arc duration when taking consideration worker extraction.
I have heard the time 2 seconds in the past. I would love to get your thoughts.
|
|
| Top |
|
 |
|
Jim Phillips (brainfiller)
|
Post subject: Re: extraction time in arc flash studies Posted: Mon May 20, 2019 9:24 am |
|
| Plasma Level |
 |
Joined: Mon Sep 17, 2007 5:00 pm Posts: 1736 Location: Scottsdale, Arizona
|
|
The two methods that are used for the arc flash duration are the clearing time of an upstream protective device or a 2 second cut off if it is feasible for a person to escape/jump back. There isn't anything regarding extraction time.
|
|
| Top |
|
 |
|
Reeberas
|
Post subject: Re: extraction time in arc flash studies Posted: Thu May 23, 2019 6:32 am |
|
Joined: Mon Apr 06, 2015 9:51 am Posts: 7
|
|
I have seen the discussion about the 2 second rule. However, if your workplace population is older and working on the bottom unit of an MCC you might be sitting on the floor, I suspect there are some people who will not have significantly moved in the two seconds. If the hazard is large because a breaker isn't tripping in the two seconds, you might want to look at the settings and sizing and see if you can lower the hazard.
|
|
| Top |
|
 |
|
Page 1 of 1
|
[ 3 posts ] |
|
|