It is currently Mon Oct 26, 2026 1:19 pm



Post new topic Reply to topic

When it comes to NFPA 70B - I have:
Heard of it 31%  31%  [ 22 ]
Have a copy 29%  29%  [ 21 ]
Read it 18%  18%  [ 13 ]
Used it 18%  18%  [ 13 ]
Never heard of it 4%  4%  [ 3 ]
Total votes : 72
Author Message
 Post subject: NFPA 70B Electrical Equipment Maintenance
PostPosted: Sun May 05, 2019 3:44 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
Since the duration of an arc flash is based on the clearing time of an upstream protective device, the condition of that device can have a significant effect on whether it operates correctly (or at all).

The words maintenance, properly maintained and condition of maintenance are found throughout NFPA 70E which states that equipment shall be maintained in accordance with manufacturers' instructions or industry consensus standards

One such industry consensus standard is NFPA 70B, Recommended Practice for Electrical Equipment Maintenance.

When it comes to NFPA 70B - I have:
Heard of it
Have a copy
Read it
Used it
Never heard of it


Select up to 4 Answers


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: NFPA 70B Electrical Equipment Maintenance
PostPosted: Mon May 06, 2019 8:31 am 
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 631
A similar question might be asked of the NETA standards.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: NFPA 70B Electrical Equipment Maintenance
PostPosted: Tue May 07, 2019 3:30 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
stevenal wrote:
A similar question might be asked of the NETA standards.


You found my play book. That's next week's question. ;)


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883