 Post subject: extraction time in arc flash studies
PostPosted: Wed May 01, 2019 12:52 pm 

Joined: Wed May 01, 2019 12:47 pm
Posts: 1
I am interested to know if there is a standard amount of time to use for arc duration when taking consideration worker extraction.

I have heard the time 2 seconds in the past. I would love to get your thoughts.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: extraction time in arc flash studies
PostPosted: Mon May 20, 2019 9:24 am 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1736
Location: Scottsdale, Arizona
The two methods that are used for the arc flash duration are the clearing time of an upstream protective device or a 2 second cut off if it is feasible for a person to escape/jump back. There isn't anything regarding extraction time.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: extraction time in arc flash studies
PostPosted: Thu May 23, 2019 6:32 am 

Joined: Mon Apr 06, 2015 9:51 am
Posts: 7
I have seen the discussion about the 2 second rule. However, if your workplace population is older and working on the bottom unit of an MCC you might be sitting on the floor, I suspect there are some people who will not have significantly moved in the two seconds. If the hazard is large because a breaker isn't tripping in the two seconds, you might want to look at the settings and sizing and see if you can lower the hazard.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883