It is currently Wed Oct 28, 2026 1:44 am



Post new topic Reply to topic

How confident are you that arc rated clothing/PPE will protect from an arc flash as expected?
High Confidence 24%  24%  [ 13 ]
Moderate/Reasonable Confidence 74%  74%  [ 40 ]
Low Level of Confidence 2%  2%  [ 1 ]
Not at all 0%  0%  [ 0 ]
Total votes : 54
Author Message
 Post subject: Arc Rated Clothing / PPE - Confidence
PostPosted: Sun Jun 30, 2019 8:13 am 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
This week’s question is part of the ongoing series about trust/confidence with various electrical protection equipment/scenarios. Here comes another one.

It is about how confident are you that arc rated clothing/PPE will protect the worker as expected in the event of an arc flash? This question assumes everything has been correctly selected.

There may be additional factors to discuss regarding this subject such as hands or other parts of the body being closer than the working distance, etc.

Here is this week’s question:
How confident are you that arc rated clothing/PPE will protect from an arc flash as expected?
-High Confidence
-Moderate/Reasonable Confidence
-Low Level of Confidence
-Not at all


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Rated Clothing / PPE - Confidence
PostPosted: Thu Sep 19, 2019 1:12 pm 
User avatar

Joined: Thu Oct 30, 2014 11:07 am
Posts: 8
Location: Ohio
If we look at ASTM F1959 - [2014] Standard Test Method for Determining the Arc Rating of Materials for Clothing, 3.1.7, the arc thermal performance value of clothing materials corelates with a 50% probability that sufficient heat transfer though the material is predicted to cause the onset of 2nd degree skin burns, ... So I guess I should be 50% confident that my 12 cal shirt will protect me from a 12 cal exposure, and 50% confident that the same exposure will cause 2nd degree burns.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883