Arc Flash Forum
Need for Single Phase Arc Flash Model
https://brainfiller.com/arcflashforum/viewtopic.php?f=33&t=5157
Page 1 of 1
Author:  Jim Phillips (brainfiller) [ Sun Aug 18, 2019 4:10 pm ]
Post subject:  Need for Single Phase Arc Flash Model
IEEE 1584 is valid for three phase arc flash calculations only.
This week’s question is about a need for a single-phase model/equations.
Would you use an IEEE single phase arc flash equations/model?
Yes
No
Not Sure
Author:  K. Engholm [ Mon Aug 19, 2019 4:37 am ]
Post subject:  Re: Need for Single Phase Arc Flash Model
I voted "not sure" We could use it but sometimes have difficulty covering all 208 volt so moving further into single phase would be quite an undertaking.
Author:  OscarPhilips [ Thu Sep 19, 2019 12:57 pm ]
For electric utility Arc-Flash Analysis, I use ArcPro for single-phase analysis per OSHA 1910.269, Appendix D, Table 3, and only use the IEEE 1584 method for three-phase open-air and enclosed studies less than 15 kV.
That said, it would be "nice" to have one approach to studies.
Author:  Flash [ Sat Oct 05, 2019 7:17 pm ]
What is typical incident energy on a 120/240 service with Arc Pro
Author:  arcad [ Mon Oct 07, 2019 5:38 am ]
You may consider the model described at http://arcadvisor.com/faq/single-phase-arc It has been implemented in ARCMASTER V1.0 software program for arc flash hazard analysis and labeling you can google online.
http://www.phpbb.com/