Which short circuit calculation method do you use?
ANSI/IEEE 72%  72%  [ 23 ]
IEC 13%  13%  [ 4 ]
Both 9%  9%  [ 3 ]
Other (please describe) 3%  3%  [ 1 ]
I Don't Perform Studies 3%  3%  [ 1 ]
Total votes : 32
Author Message
 Post subject: Short Circuit Calculations: ANSI/IEEE or IEC
PostPosted: Sun Sep 15, 2019 12:47 am 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
I just arrived in Geneva, Switzerland for IEC meetings which prompted this week's question. It is about IEC vs. ANSI/IEEE Standards for short circuit current calculations.

Depending on which method is used, the results can vary a bit which may also affect the calculated incident energy.

Here is this week's question:

Which short circuit calculation method do you use?

ANSI/IEEE
IEC
Both
Other (please describe)
I Don't Perform Studies


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Short Circuit Calculations: ANSI/IEEE or IEC
PostPosted: Sun Sep 15, 2019 7:41 pm 
Sparks Level
User avatar

Joined: Wed Jun 10, 2009 5:00 pm
Posts: 271
Location: Toronto
Jim Phillips (brainfiller) wrote:
I just arrived in Geneva, Switzerland for IEC meetings which prompted this week's question. It is about IEC vs. ANSI/IEEE Standards for short circuit current calculations.

Depending on which method is used, the results can vary a bit which may also affect the calculated incident energy.

Here is this week's question:

Which short circuit calculation method do you use?

ANSI/IEEE
IEC
Both
Other (please describe)
I Don't Perform Studies


I prefer comprehensive method factoring in all the equipment active, reactive impedance and contribution to fault current. Also, I find it important to know the range of available fault current (min - max) and take into account arc duration so I can identify worst case arc flash scenario. Incident energy alone is meaningless unless you know how fast that energy has been delivered. Jim, let me know please if I can be of any help elaborating on or escalating this issue to decision making authorities.

_________________
Michael Furtak, C.E.T.
http://arcadvisor.com


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883