When was the first time you (or consultant) performed an arc flash study?
Before 2000 (when?) 3%  3%  [ 2 ]
2000 – 2004 26%  26%  [ 15 ]
2004 – 2009 36%  36%  [ 21 ]
2009 – 2012 12%  12%  [ 7 ]
After 2012 21%  21%  [ 12 ]
Does not apply 2%  2%  [ 1 ]
Total votes : 58
Author Message
 Post subject: First Arc Flash Study - When?
PostPosted: Sun Dec 15, 2019 6:34 am 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
Some of the first arc flash studies were performed before IEEE 1584 was first published in 2002 using tables and/or published articles that were available.

The 1995 Edition of NFPA 70E first introduced the term “Arc Flash� and the 2000 Edition introduced the Arc Flash Boundary (Flash Protection Boundary) as well as PPE Tables (HRC back then) 2004 Edition of NFPA 70E first acknowledged the use of IEEE 1584.

When was the first time you (or consultant) performed an arc flash study?

Before 2000 (when?)
2000 – 2004
2004 – 2009
2009 – 2012
After 2012
Does not apply


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: First Arc Flash Study - When?
PostPosted: Fri Jan 24, 2020 6:42 am 

Joined: Wed Jul 25, 2012 11:41 am
Posts: 12
Location: Halifax, NS
I helped develop my first arc flash model in ETAP when I was a co-op student back in the summer of 2004. I really had no idea what I was doing, and there was only one engineer in the office that really had an idea what it was trying to achieve.

The study was for a local university when they were completing an upgrade to one of their pieces of 600V switchgear.

_________________
Jeff M
My Electrical Safety Page


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883