 Post subject: Arc Flash Study : Generator Fault Contribution
PostPosted: Tue Apr 28, 2020 11:23 am 

Joined: Tue Dec 17, 2019 10:00 am
Posts: 12
Good day all

In some cases, an arc flash study may need to be performed on some systems with generator supply.

I am curious how do you handle this , bearing in mind that the generator fault contribution happens over transient , sub-transient and steady states.

Higher fault currents (sub-transient) result in shorter tripping times hence lower incident energy values while lower fault currents (transient states) have longer trip times results in high incident energy values.

What is your approach when dealing with synchronous machine (generator supplies) with regards to arc flash studies ?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Study : Generator Fault Contribution
PostPosted: Thu Apr 30, 2020 9:20 am 
Sparks Level
User avatar

Joined: Wed Jun 10, 2009 5:00 pm
Posts: 271
Location: Toronto
Ashdgee wrote:
Good day all

In some cases, an arc flash study may need to be performed on some systems with generator supply.

I am curious how do you handle this , bearing in mind that the generator fault contribution happens over transient , sub-transient and steady states.

Higher fault currents (sub-transient) result in shorter tripping times hence lower incident energy values while lower fault currents (transient states) have longer trip times results in high incident energy values.

What is your approach when dealing with synchronous machine (generator supplies) with regards to arc flash studies ?


I would run both case scenarios and consider the worst case scenario for PPE selection and labeling. Please note that contrary to common belief and so called "scientific consensus", the highest incident energy does not necessarily mean the highest hazard. Please google "Evaluation of Onset to Second Degree Burn Energy in Arc Flash" for more information.

_________________
Michael Furtak, C.E.T.
http://arcadvisor.com


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883