Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
Arc Flash Labels continue to evolve. NFPA 70E 130.5(H)(3) requires at least one of the following on the label:

-Available incident energy and the corresponding working distance OR PPE Category
-Minimum arc rating of clothing
-Site Specific Level of PPE


What do you list on your/client’s labels for PPE? Select all that apply
Incident energy and working distance
PPE Category
Arc Rating
Site Specific Level of PPE
No Labels


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: What do you list on your/client’s labels for PPE?
PostPosted: Tue May 05, 2020 9:56 am 

Joined: Tue Jun 18, 2013 5:00 pm
Posts: 10
We do not produce labels for anything other than an incident energy analysis. We submit IE and working distance on labels.

We do not include PPE catagory per NFPA 70E (2018) 130.5 (F) and (H)(3) "The results of an incident energy analysis to specify an arcflash PPE category in Table 130.7 (C) (15) (c) shall not be permitted." [We think we have these interpreted correctly, IE and PPE Catagory seem to be mutually exclusive.]
Nor have we invoked 130.5 (H) exception No2 for industrial installations.

We also include the equipment ID of the label location and the lineside feeder device ID for isolation and lockout.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883