The 2017 Edition of the National Electrical Safety Code (IEEE C2) contains Table 410-1 Clothing and clothing systems for voltages 50 V to 1000V (ac).

This table lists the maximum arc rating necessary for protection from the arc flash hazard based on equipment type.

4 cal/cm^2 is listed for panelboards 50V to 250 V

Note (1) [applies to entire table]
This table was developed from fault testing based on equipment type and is independent of fault current unless otherwise noted.

Note (2) [specific 50 V – 250 V panelboards]
The arc rating values for the panels are based on industry testing by two separate major utilities and one research institute and that the arc will not sustain more than 2 cycles.

This week’s question:

Have you used 4 cal/cm^2 from NESC Table 410-1 for panels up to 250V?
Yes
No
Never heard of it


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Maximum 4 cal/cm^2 for panels to 250 Volts? NESC 410-1
PostPosted: Mon Oct 12, 2020 7:38 am 
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 536
Note the scope of the NESC prior to use. It may not be appropriate for many forum members.


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Maximum 4 cal/cm^2 for panels to 250 Volts? NESC 410-1
PostPosted: Mon Oct 12, 2020 7:59 am 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1517
Location: Scottsdale, Arizona
To add to the discussion: OSHA letter of interpretation


Report this post
Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You can post new topics in this forum
You can reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883