Maximum 4 cal/cm^2 for panels to 250 Volts? NESC 410-1
https://brainfiller.com/arcflashforum/viewtopic.php?f=33&t=5370
Page 1 of 1

Author:  Jim Phillips (brainfiller) [ Sun Oct 11, 2020 11:30 am ]
Post subject:  Maximum 4 cal/cm^2 for panels to 250 Volts? NESC 410-1

The 2017 Edition of the National Electrical Safety Code (IEEE C2) contains Table 410-1 Clothing and clothing systems for voltages 50 V to 1000V (ac).

This table lists the maximum arc rating necessary for protection from the arc flash hazard based on equipment type.

4 cal/cm^2 is listed for panelboards 50V to 250 V

Note (1) [applies to entire table]
This table was developed from fault testing based on equipment type and is independent of fault current unless otherwise noted.

Note (2) [specific 50 V – 250 V panelboards]
The arc rating values for the panels are based on industry testing by two separate major utilities and one research institute and that the arc will not sustain more than 2 cycles.

This week’s question:

Have you used 4 cal/cm^2 from NESC Table 410-1 for panels up to 250V?
Yes
No
Never heard of it

Author:  stevenal [ Mon Oct 12, 2020 7:38 am ]
Post subject:  Re: Maximum 4 cal/cm^2 for panels to 250 Volts? NESC 410-1

Note the scope of the NESC prior to use. It may not be appropriate for many forum members.

Author:  Jim Phillips (brainfiller) [ Mon Oct 12, 2020 7:59 am ]
Post subject:  Re: Maximum 4 cal/cm^2 for panels to 250 Volts? NESC 410-1

To add to the discussion: OSHA letter of interpretation