Do you wear arc rated PPE when Table 130.5(C) states NO likelihood of occurrence of an arc flash?
Yes
No
Sometimes – It depends (please comment)
You may select 1 option

View results
Author Message
 Post subject: Arc Rated PPE - Likelihood of Occurrence of Arc Flash = No
PostPosted: Sun Jan 24, 2021 3:46 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1574
Location: Scottsdale, Arizona
This week’s question is a variation on one that I asked a couple of weeks ago.

NFPA 70E Table 130.5(C) Estimate of the Likelihood of Occurrence of an Arc Flash Incident lists operation of a circuit breaker, switch, contactor, or starter as “NO” for likelihood of occurrence of an arc flash for “Normal Equipment Condition.”

Normal condition is defined by 110.4(D) and includes the equipment being properly installed, properly maintained, used in accordance with instructions, doors are closed and secured, covers in place, no evidence of impending failure.

With that intro, here is this week’s question:

Do you wear arc rated PPE when Table 130.5(C) states NO for likelihood of occurrence of an arc flash?
Yes
No
Sometimes – It depends (please comment)


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Rated PPE - Likelihood of Occurrence of Arc Flash =
PostPosted: Mon Jan 25, 2021 8:43 am 
Sparks Level
User avatar

Joined: Tue Oct 26, 2010 5:00 pm
Posts: 195
Location: Maple Valley, WA.
Our company policy is that if we are working around energized equipment, then we always wear AR clothing, even if the AF level is less than 1.2 Cal/cm2.

_________________
Robert Fuhr, P.E.; P.Eng.
PowerStudies


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Rated PPE - Likelihood of Occurrence of Arc Flash =
PostPosted: Mon Jan 25, 2021 9:29 am 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1574
Location: Scottsdale, Arizona
Robertefuhr wrote:
Our company policy is that if we are working around energized equipment, then we always wear AR clothing, even if the AF level is less than 1.2 Cal/cm2.


That's the comment I was hoping to hear! Thanks Bob!


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Rated PPE - Likelihood of Occurrence of Arc Flash =
PostPosted: Sat Jan 30, 2021 6:59 am 

Joined: Fri Jul 10, 2009 10:14 am
Posts: 30
Location: West Central, OH
Our company policy is when interacting with energized equipment, proper PPE for arc flash hazards must be worn. Might be more than needed but trying to teach everybody how to ensure electrical equipment meets the requirements for not needing PPE seemed very onerous. Teach that even wearing arc rated PPE per the label can result in injury.


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Rated PPE - Likelihood of Occurrence of Arc Flash =
PostPosted: Wed Mar 24, 2021 1:06 pm 
Sparks Level

Joined: Sat Nov 21, 2009 10:23 pm
Posts: 113
Location: Ohio
Jim


do you want to comment on the 2021 70E removing the <= 1.2 cal table.


Jim Phillips (brainfiller) wrote:
Robertefuhr wrote:
Our company policy is that if we are working around energized equipment, then we always wear AR clothing, even if the AF level is less than 1.2 Cal/cm2.


That's the comment I was hoping to hear! Thanks Bob!


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Rated PPE - Likelihood of Occurrence of Arc Flash =
PostPosted: Sun Mar 28, 2021 3:05 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1574
Location: Scottsdale, Arizona
Flash wrote:
Jim


do you want to comment on the 2021 70E removing the <= 1.2 cal table.


Jim Phillips (brainfiller) wrote:
Robertefuhr wrote:
Our company policy is that if we are working around energized equipment, then we always wear AR clothing, even if the AF level is less than 1.2 Cal/cm2.


That's the comment I was hoping to hear! Thanks Bob!


I'm assuming you meant PPE Category 0 which was < 1.2 cal/cm2?
The requirements for Category 0 were already inherent in NFPA 70E i.e. eye protection, natural fiber etc. so it was removed in 2015. - let me know if I misunderstood the question.


Report this post
Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 6 posts ] 

All times are UTC - 7 hours


You can post new topics in this forum
You can reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883