Do you believe 208 V systems pose an arc flash hazard?
Yes
No
Depends
You may select 1 option

View results
Author Message
 Post subject: Arc Flash Hazard at 208 Volts?
PostPosted: Sun Feb 14, 2021 9:18 am 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1561
Location: Scottsdale, Arizona
NOTE: Results and comments from this survey do not represent recommendations.

There is still quite a bit of discussion regarding arc flash hazards at 208 volts.

This week’s question is simple.

Do you believe 208 V systems pose an arc flash hazard?

Yes
No
Depends


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Hazard at 208 Volts?
PostPosted: Sun Feb 21, 2021 2:34 pm 

Joined: Sun Feb 21, 2021 2:27 pm
Posts: 1
Jim, I have had several persons indicate their belief that arc flash hazard doesn't exist at 208 VAC because it does not sustain. This seems wrong to me for two reasons: 1) anecdotal evidence (real injurious arc flash events) prove otherwise, and 2) IEEE 1584 does not indicate that we should not be calculating the IE at 208 VAC. Some of these people seem to be "quoting" persons like yourself, but I think they are misquoting. My questions to you:

1) Do you support the IEEE 1584 calculations at 208 VAC?

2) Can you post some proof of real events of 208 VAC arc flash?


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Hazard at 208 Volts?
PostPosted: Mon Feb 22, 2021 11:25 am 
User avatar

Joined: Mon May 25, 2015 1:17 pm
Posts: 16
Location: Northern California
Forgive me for not backing this up with a specific reference but I recall that 2019 IEEE 1584 discusses 2000 amps as being a point where arc flash is a hazard on 208V systems. I include labels for all 120/208V systems as if it is not a hazard then that is what the label valuably communicates.


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Hazard at 208 Volts?
PostPosted: Mon Feb 22, 2021 12:45 pm 
Sparks Level
User avatar

Joined: Tue Oct 26, 2010 5:00 pm
Posts: 195
Location: Maple Valley, WA.
In large cities, the utilities will use (3) Network transformers (with 208 V secondary) that are paralleled. The available fault current can be well over 100 kA. At these locations, there is definitely an Arc Flash (and blast) hazard. However, a low power source such as a 45 kVA 480 - 208 V distribution transformer most likely will not have enough energy to have a arc flash be self sustaining.

This is why I voted "Depends" because it really depends on the energy source (and equipment construction i.e. bus gap) as to whether the arc flash event will be self sustaining.

_________________
Robert Fuhr, P.E.; P.Eng.
PowerStudies


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Hazard at 208 Volts?
PostPosted: Sun Feb 28, 2021 3:37 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1561
Location: Scottsdale, Arizona
A bit of a TRICK QUESTION. (sorry)

This is just my view/opinion and not anything official from a particular standard.

- IEEE 1584 has the 2000A / 208 Exception (formerly 125 kVA transformer)
- NFPA 70E doesn't require arc rated PPE until the incident energy is ABOVE 1.2 cal/cm^2.

Because of the two statements above, some have come to believe "No Arc Flash Hazard Exists" for those cases. The results of the survey seem to indicate that might be the sentiment as well.

I look at work on any energized equipment - EVEN with lower incident energy (NFPA 70E) or low short circuit current (2000A IEEE 1584) as STILL being an arc flash hazard. The key is it may not be considered a major arc flash hazard but there can still be injury.

Case in point: I have run into situations where there are small burns on the finger(s), hand etc. from these low level arc flash events. Not life threatening but painful and an injury.

Also, don't forget the incident energy increases with reduced distance (getting closer to the equipment) so even if an arc flash label states the incident energy is less than 1.2 cal/cm^2, it is based on the working distance - typically 18, 24 or 36 inches. Any part of the body closer than that and the incident energy increases!

So, again my opinion but: don't ever use the language "No Arc Flash Hazard Exists" unless the system is in an electrically safe work condition.

Your thoughts? Fire Away! :)


Report this post
Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You can post new topics in this forum
You can reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883