 Post subject: Maximum number of arc flash labels at one location
PostPosted: Sun Jul 18, 2021 10:57 am 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1620
Location: Scottsdale, Arizona
This week’s question was asked years ago but it keeps coming up. Most recently in a committee technical discussion. It is similar to last week’s question: How should incident energy from arc energy reduction methods be addressed on arc flash labels?

This week’s question is about the number of DIFFERENT LABELS at the SAME LOCATION for different scenarios. i.e. a label for normal, a label for maintenance mode, a label for….
So here goes:

What is the maximum number of DIFFERENT arc flash labels have you seen/used at the SAME location?

1
2
More than 2
Doesn’t apply

How many DIFFERENT labels have you seen/used at the SAME location? (read the whole post first)


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Maximum number of arc flash labels at one location
PostPosted: Sun Jul 18, 2021 5:22 pm 
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 544
Location: Wisconsin
I have installed labeling for three different scenarios.

It is amazing what I will do for money.


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Maximum number of arc flash labels at one location
PostPosted: Wed Jul 21, 2021 12:02 pm 
Sparks Level
User avatar

Joined: Tue Apr 17, 2012 8:19 am
Posts: 250
Location: Charlotte, NC
When I was doing the labels for the solar power grid tie inverters, there was 1 label for each opening in the inverter enclosure (there are 10 doors / access panels for the enclosure) for the installed production parameters (4 MW transformer, no fuses). There is a second set of labels for testing in our facility for the operational testing parameters (500 kW transformer, with semiconductor fuses, and a breaker disconnect).


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Maximum number of arc flash labels at one location
PostPosted: Wed Jul 28, 2021 8:44 am 
Sparks Level
User avatar

Joined: Tue Apr 17, 2012 8:19 am
Posts: 250
Location: Charlotte, NC
to clarify my earlier post: The incident energy ranged from below 1 cal/cm^2 to 75 cal/cm^2, depending on which particular door / panel you opened


Report this post
Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


You can post new topics in this forum
You can reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883