Arc Flash Forum
Arc Flash Label Data - Revisted
https://brainfiller.com/arcflashforum/viewtopic.php?f=33&t=5522
Page 1 of 1
Author:  Jim Phillips (brainfiller) [ Sun Oct 24, 2021 12:57 pm ]
Post subject:  Arc Flash Label Data - Revisted
Arc flash (equipment) labels and data have been discussed in the past but practices evolve over time.
The 2021 Edition of NFPA 70E has minimum requirements for labels which includes:
(1) Nominal System Voltage 130.1(H)(1)
(2) Arc Flash Boundary 130.1(H)(2)
(3) At least one of the following:
a. Available incident energy and the corresponding working distance OR the arc flash PPE category
b. Minimum arc rating of clothing
c. Site-specific level of PPE
Here are a couple of references regarding labeling:
Article: Arc Flash Labels Simplified
Arc Flash Labeling Requirements and Strategies Free On Demand Video Class
To gauge the evolution of labeling, this week’s question is a follow up to a similar question asked quite some time ago.
What are your/company preferences for arc flash labels?
• Nominal Voltage
• Arc Flash Boundary
• Incident Energy and Working distance
• Arc Flash PPE Category
• Minimum arc rating of clothing
• Site specific PPE level
• Limited and Restricted approach boundary
• Date
• List of PPE requirements
• Something else - please tell us!
Author:  Robertefuhr [ Mon Oct 25, 2021 10:33 am ]
Post subject:  Re: Arc Flash Label Data - Revisted
We also include the following items:
1. Our company name.
2. Our company phone number.
3. Our Job #. (this is helpful for when we do a AF refresh study after 5 years.)
4. Maximum available fault current.
5. Standard Version used to calculate the AF energy and boundaries.
Author:  stevenal [ Mon Oct 25, 2021 1:04 pm ]
I would add that Robert's example above also contains an ANSI signal word and symbol.
Author:  phil.haataja [ Tue Oct 26, 2021 7:54 am ]
Having the maximum available fault current is a huge plus. I think by adding that number people will gain a much better appreciation of what arc flash energy is all about. Strangely, too many people order gear without even knowing what the available fault current even is.