rmgbob wrote:
I have been meaning to ask this so this seems a good time as any considering the question.
Lets say we have a dry type transformer, 480-120/208 that serves a MCB panel. I have applied 2-seconds at this panel in these cases. Now lets say we have sub panels served by breakers in this panel. Would the 2-seconds apply for the sub panels too? Technically they are being served by this transformer, but through a couple breakers along the way. Where would you draw the line, especially if the sub panel is a long feeder run with a high incident energy because of it. If the calculations are allowed to run, it indicates about a 4-second clearing time. Curious on thoughts.
Two seconds is considered the amount of time it takes for a person to fall away from the arcing incident, so yes, it is logical to use that value for everything, except where the fall away could be prevented - like in a bucket truck.
But it's also somewhat unique for a breaker to hold during an arcing fault where there's not enough current to make it trip.
There was a fellow who taught that one should use a 1000-second trip time, and then explore those cases where 1000 seconds occurred and make adjustments to assure tripping. Then readjust the Study for the 2-second timeout. I know because someone in our group forgot about returning to the 2-second value and that created a label that had a 1/4 mile arc flash boundary.
Good luck with your Studies.