Lauri1232000
|
Post subject: Arc Flash Assessment Required at 208v Posted: Fri Nov 10, 2023 6:04 am |
|
|
Currently in the middle of a safety audit in Europe. Arc flash study completed in 2017 and the auditor says it is not compliant because the arc flash study did not consider equipment >208 Volts but < 240 volts. Is arc flash study required for equipment >208 volts but less than 240.
Bonus points if you include the standard reference.
TIA,
Tired Safety Manager
|
|
Top |
|
 |
mpparent
|
Post subject: Re: Arc Flash Assessment Required at 208v Posted: Mon Nov 13, 2023 9:37 am |
|
Joined: Thu Apr 18, 2019 11:42 am Posts: 163
|
I would say the short answer is "yes". The voltage range you are talking about is within the bounds of IEEE 1584. What is the specific utilization voltage you are using?
Mike
|
|
Top |
|
 |
Guest
|
Post subject: Re: Arc Flash Assessment Required at 208v Posted: Thu Nov 16, 2023 7:24 am |
|
|
Even if it uses the DGUV 203-077 method for arc flash calculation, the method is applicable over 50V; so the calculation should have been done. It may depend on the electrical safety standards of the exact country you are talking about.
|
|
Top |
|
 |
HarryPotter69
|
Post subject: Re: Arc Flash Assessment Required at 208v Posted: Sat Mar 30, 2024 4:24 am |
|
Joined: Sat Mar 30, 2024 4:22 am Posts: 1
|
In Europe, arc flash studies typically cover equipment operating above 208 volts. The range you mentioned (208-240 volts) should indeed be included in the study. Standards like IEC 61482 provide guidelines. Make sure all relevant equipment and voltage ranges are considered for safety assessments.
_________________ Yeonmi
|
|
Top |
|
 |
bubblyeducate
|
Post subject: Re: Arc Flash Assessment Required at 208v Posted: Mon Jan 13, 2025 8:20 pm |
|
Joined: Mon Jan 13, 2025 8:18 pm Posts: 1
|
Lauri1232000 wrote: Currently in the middle of a safety audit in Europe. Arc flash study completed in 2017 and the auditor says it is not compliant because the arc flash study did not consider equipment >208 Volts but < 240 volts. Is arc flash study required for equipment >208 volts but less than 240. Bonus points if you include the standard reference. geometry dash TIA,
Tired Safety Manager
Yes, an arc flash study is required for equipment operating between 208V and 240V, but whether the study must cover these voltages depends on several factors, including standards and local regulations.
|
|
Top |
|
 |
pantheonbruise
|
Post subject: Re: Arc Flash Assessment Required at 208v Posted: Tue Jan 14, 2025 6:25 pm |
|
Joined: Tue Jan 14, 2025 6:20 pm Posts: 1
|
HarryPotter69 wrote: In Europe, arc flash studies typically cover equipment operating above 208 volts. The range you mentioned (208-240 volts) should indeed be included in the study. Standards like IEC 61482 provide guidelines. Make sure all relevant equipment and voltage ranges are considered for safety assessments. Hello. I am wondering why arc flash studies in Europe usually focus on equipment operating above 208 volts and why the 208-240 volt voltage range needs to be included in the studies?
_________________ geometry dashlossstarry@gmail.com
|
|
Top |
|
 |
Terry Becker
|
Post subject: Re: Arc Flash Assessment Required at 208v Posted: Sat Jan 18, 2025 7:36 pm |
|
Joined: Sun Sep 23, 2007 5:00 pm Posts: 148 Location: Calgary, Alberta, Canada
|
208VAC three phase with short circuit current greater than 2000A. Not required for single phase 240VAC.
|
|
Top |
|
 |
cameliab
|
Post subject: Re: Arc Flash Assessment Required at 208v Posted: Sun Jul 27, 2025 12:55 pm |
|
Joined: Sun Jul 27, 2025 12:51 pm Posts: 1
|
Lauri1232000 wrote: Currently in the middle of a safety audit in Europe. Arc flash study completed in 2017 and the auditor says it is not compliant because the arc flash study did not consider equipment >208 Volts but < 240 volts. Is arc flash study required for equipment >208 volts but less than 240.
Bonus points if you include the standard reference. change clothes of photo online free
TIA,
Tired Safety Manager
Great question—yes, arc flash studies are generally required for equipment operating above 50 volts, depending on available fault current and clearing time. Equipment >208V but <240V can still pose arc flash risk, so it should be evaluated per NFPA 70E standards. Also, I recently used a tool to change clothes of photo online free—surprisingly accurate for visual edits!
|
|
Top |
|
 |
|