Hi everyone, hope you and yours are doing great.

I have a question regarding the electrode configuration of one distribution switchboard similar to the picture attached.

There you will find in the upper part of the picture a branch circuit breaker. Also, going down the distribution bus there are connected around 8 branch circuit breakers (4 left + 4 right).

My concern is that the bars connecting the line side of the branch circuit breakers seem to me as an horizontal electrode configuration because the worker would stand practically in front of them.

What do you think? Seems to you also HCB configuration?

Kind Regards to all,


Ivan


Attachments:
File comment: Front side of the switchboard equipment.
SWBRD-001.jpeg
SWBRD-001.jpeg [ 114.46 KiB | Viewed 367 times ]
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Electrode Configuration??
PostPosted: Tue Jun 08, 2021 5:31 am 

Joined: Thu Apr 18, 2019 11:42 am
Posts: 49
Sounds reasonable. You could always calculate worst-case and use that.

Mike


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883