It is currently Tue Apr 28, 2026 6:33 pm



Post new topic Reply to topic
Author Message
 Post subject: Entering in Fault Current Information
PostPosted: Mon Oct 14, 2024 6:06 am 

Joined: Wed Jun 12, 2024 5:19 am
Posts: 35
Good morning,
Can someone help me with entering this into SKM?


Attachments:
Fault Current Information.jpg
Fault Current Information.jpg [ 85.42 KiB | Viewed 1170933 times ]
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Entering in Fault Current Information
PostPosted: Mon Oct 14, 2024 9:24 am 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 488
Location: Indiana
That data sheet looks like it's from Duke and I'd bet money the %Z is not actual but straight out of the Duke red book instead. Some of their transformers have the nameplate on the outside, not in the secondary compartment. Not many, but some do. I'd check that if you can. If you ask them for actual %Z they probably won't respond or provide it so about all you can do is use the 5.32% or run multiple scenarios and worse case.

I sent you a video I made that touches on this. It's one I made a couple years ago but took it down as I left out some stuff that should have been included and it just wasn't a very good video to start with. Hope it helps.

_________________
SKM jockey for hire
PE in 17 states


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Entering in Fault Current Information
PostPosted: Mon Oct 14, 2024 12:30 pm 

Joined: Wed Jun 12, 2024 5:19 am
Posts: 35
Yes, its from Duke.
Thank you for the video!


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Entering in Fault Current Information
PostPosted: Wed Oct 16, 2024 6:52 am 
Sparks Level

Joined: Thu Apr 18, 2019 11:42 am
Posts: 175
In these cases, I'll use +/-7.5% of the Z given by the utility when I suspect the # is canned. Then run scenarios around those #'s as Brent suggested.

Mike


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Entering in Fault Current Information
PostPosted: Wed Feb 26, 2025 5:33 am 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 488
Location: Indiana
A video I made yesterday reminded me of this thread. Check it out if interested. Here's the link: https://www.youtube.com/watch?v=5TPIOAX6Ksk

_________________
SKM jockey for hire
PE in 17 states


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883