 Post subject: Relay modeling
PostPosted: Mon Jan 26, 2026 11:24 am 

Joined: Thu Dec 18, 2025 3:21 pm
Posts: 7
Do you model anything other than 50/51 settings for relays?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Relay modeling
PostPosted: Tue Jan 27, 2026 4:24 am 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 461
Location: Indiana
The CT ratio, curve type, any time delays or definite time setting and the breaker clearing time.

_________________
SKM jockey for hire
PE in 17 states


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Relay modeling
PostPosted: Tue Jan 27, 2026 6:13 am 

Joined: Thu Dec 18, 2025 3:21 pm
Posts: 7
Thanks! What about upstream transformer differential protection and generator protection. Will these affect the arc flash calculations?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Relay modeling
PostPosted: Tue Jan 27, 2026 7:12 am 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 461
Location: Indiana
Just depends on what the settings are and what breaker or breakers they are controlling and what other protection downstream busses have or don't have. I do model them and include the settings for record if nothing else but it is possible that they will affect IE, again, just depends on the setup.

_________________
SKM jockey for hire
PE in 17 states


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883