 Post subject: 130.3 Exception No. 1
PostPosted: Wed Apr 14, 2010 11:14 am 
Offline

Joined: Tue Nov 03, 2009 10:03 am
Posts: 3
If a system meets all conditions listed in Exception No. 1, an arc flash hazard analysis is not required.

Say the system is at 120 volts and meets all conditions in Exception No. 1, does the arc flash boundary move to the 4ft default boundary? Or is there no arc flash boundary?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Apr 20, 2010 12:42 pm 
Offline
Sparks Level

Joined: Mon Dec 14, 2009 4:24 pm
Posts: 61
A strict interpretation of the standard seems to require the 4 foot boundary for this case.

However, 130.3(B)(2) implies that you can use the task table to select PPE inside the 4 foot boundary. If the table recommends HRC0 for the task you want to do inside the 4 foot boundary then the impact seems negligible.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Jun 22, 2010 6:05 am 
Offline
User avatar

Joined: Fri Oct 02, 2009 4:27 am
Posts: 6
Location: New Hampshire
Can you use the exceptions?

If you meet all of the criteria for Exception No. 1, but determine that your incident energy is over 100kA cycles, are you now required to perform the calculations? 130.3 (A)(1)?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Jun 22, 2010 6:23 am 
Offline
Sparks Level

Joined: Mon Mar 29, 2010 11:52 am
Posts: 110
Location: Yankton SD/ Lead SD
Yes, you would then be required to calculate the FP boundary.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Jun 22, 2010 7:15 am 
Offline
User avatar

Joined: Fri Oct 02, 2009 4:27 am
Posts: 6
Location: New Hampshire
If you are required to calculate the FPB if over 100kA cycles, whats the point of the exception? Either way you are going to have run calculations to determine whether or not you meet the 100kAC. Thus negating the exception to not have to.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Jun 22, 2010 8:29 am 
Offline
Sparks Level

Joined: Mon Mar 29, 2010 11:52 am
Posts: 110
Location: Yankton SD/ Lead SD
seriouswatts wrote:
If you are required to calculate the FPB if over 100kA cycles, whats the point of the exception? Either way you are going to have run calculations to determine whether or not you meet the 100kAC. Thus negating the exception to not have to.


I did not say that the exception made any logical sense, just that the exception exists.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Jun 22, 2010 12:44 pm 
Offline
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 445
Location: Wisconsin
seriouswatts wrote:
If you are required to calculate the FPB if over 100kA cycles, whats the point of the exception? Either way you are going to have run calculations to determine whether or not you meet the 100kAC. Thus negating the exception to not have to.


Technically, determing the 'kA cycles' is a short circuit and coordination analysis not an 'arc flash analysis'. :D :rolleyes:


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Jun 24, 2010 3:54 am 
Offline
User avatar

Joined: Fri Oct 02, 2009 4:27 am
Posts: 6
Location: New Hampshire
A SSC/PDC study would give you your interrupting current to size your equipment (kAIC). The kA cycles is more for arc flash becasue you are concerned with the opening time of the device relative to the amount of fault current available.
My point is really, that you can meet all of the criteria for exception one to not have to do an arc flash analysis, but if you have low fault current your OCPD opening time could be long, and thus over the 100kA cycles. So either way you have run calculations, you can't just blindly take the exception.

Does that sound right?


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 8 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 4 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883