 Post subject: Need recommendations
PostPosted: Sat Apr 24, 2010 8:22 pm 
Offline

Joined: Sat Nov 21, 2009 3:10 pm
Posts: 25
I have a 3000kVA utility transformer with its secondary connected directly to the main switchgear bus. When I run the arc flash it produces an incident energy of 150 cal/cm^2. Any recommendations as to how I can lower that incident energy? With the transformer connected directly to the bus there doesn't appear to be a place to install a main circuit breaker or anything. I am kind of stumped on this one. Any help would be greatly appreciated.

Thanks in advance!


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sun Apr 25, 2010 6:51 am 
Offline
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
bruinfan wrote:
I have a 3000kVA utility transformer with its secondary connected directly to the main switchgear bus. When I run the arc flash it produces an incident energy of 150 cal/cm^2. Any recommendations as to how I can lower that incident energy? With the transformer connected directly to the bus there doesn't appear to be a place to install a main circuit breaker or anything. I am kind of stumped on this one. Any help would be greatly appreciated.

Thanks in advance!


You have a common problem and thee are a few mitigation solutions, In fact I am presenting mitigation mitigation solutions at a conference in 2 hours on this very issue. First thing to look at is your primary fuse, there may be some older types that will work much better. If not you can replace your primary fuse with a mini VCB that uses current inputs from the secondary side of the transformer.

Remote racking and switchnig may be the right solution too, depending on your needs.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Apr 26, 2010 8:25 pm 
Offline
Arc Level

Joined: Thu Jan 10, 2008 8:49 pm
Posts: 483
Location: New England
I think S&C was making electronic fuses that have programable trip points. You could try to work in a CB on the primary but have the CTs on the secondary. Also, check the fuse catalogs to see if there is a faster one.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Apr 27, 2010 1:11 pm 
Offline

Joined: Thu Feb 11, 2010 5:51 pm
Posts: 22
Location: Great White North
haze10 wrote:
I think S&C was making electronic fuses that have programable trip points. You could try to work in a CB on the primary but have the CTs on the secondary. Also, check the fuse catalogs to see if there is a faster one.


Here is a link to S/C fault fiter electronic fuse arrangement.I plugged this into our arc flash program and it reduced the main board from 170 cal to 48 cal.


http://www.sandc.com/products/faultfiter/default.asp


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 4 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883