ekstra   ara
 Post subject: Does this make sense? If so, then how?
PostPosted: Thu Apr 29, 2010 10:55 am 
Offline

Joined: Thu Apr 29, 2010 10:49 am
Posts: 7
If I have a 225kVA 4.16kv/480V xfmr in my model and I run arc-flash using ETAP.

Is it possible that the high side gets a lower HRC than the secondary side?

Let's say there is a 50E fuse on the primary side.

The results come back as Cat 0 for the primary side and Cat 1 on the secondary side.

I am hesistant to put a Cat 0 stick on the primary side. Is there something wrong with my calculations or is this normal? I have seen this in a few other studies as well.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Apr 29, 2010 1:36 pm 
Offline
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 442
Yes. Arc flash is current Dependant, and you have much less on the primary side.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Apr 29, 2010 1:45 pm 
Offline
Arc Level

Joined: Wed Jun 04, 2008 9:17 am
Posts: 411
Location: Spartanburg, South Carolina
And probably faster clearing.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri May 14, 2010 6:41 am 
Offline

Joined: Thu Apr 29, 2010 10:49 am
Posts: 7
I just found that to be kind of strange to have a low primary side but a really high secondary side when I am dealing with transformers in ETAP


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri May 14, 2010 6:46 am 
Offline
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
titan wrote:
I just found that to be kind of strange to have a low primary side but a really high secondary side when I am dealing with transformers in ETAP


Normal to see that. A fault on the secondary side before the OCPD will rely on the primary fuses to clear the fault, but they will see much lower current levels on the other side of the transformer and have a long clearing time.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu May 20, 2010 1:56 pm 
Offline

Joined: Thu Apr 29, 2010 10:49 am
Posts: 7
Wouldn't the current levels be higher?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu May 20, 2010 6:28 pm 
Offline
Arc Level

Joined: Wed Jun 04, 2008 9:17 am
Posts: 411
Location: Spartanburg, South Carolina
titan wrote:
Wouldn't the current levels be higher?


Current level is inversely proportional to voltage level.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu May 20, 2010 7:45 pm 
Offline
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 445
Location: Wisconsin
titan wrote:
I just found that to be kind of strange to have a low primary side but a really high secondary side when I am dealing with transformers in ETAP


Most people are surprised that the secondary AFIE is so high compared to the primary. This is the reason that service entrance locations are usually aove 40 cal/cm┬▓. And why the 'task table' should not be used for these locations.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 8 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883