titan wrote:
I just found that to be kind of strange to have a low primary side but a really high secondary side when I am dealing with transformers in ETAP
Normal to see that. A fault on the secondary side before the OCPD will rely on the primary fuses to clear the fault, but they will see much lower current levels on the other side of the transformer and have a long clearing time.