 Post subject: Calculations for 208v System
PostPosted: Thu Jul 22, 2010 5:24 am 
Offline
Sparks Level

Joined: Tue May 18, 2010 7:03 am
Posts: 53
I have read about the exemption for <240V and <125kva transformer. Also have read about the accuracy of each calculation method for different voltage levels. I have come across a situation where the transformer is 225kva, 12kv to 208v for a small pumping station. Which calculation method is most accurate for this? Turns out the 225 kva transformer is large because it feeds a variety of other loads in addition to the substation. The utility has given me a transformer fault current of 28,400A for the secondary side.

Typically the transformers are fairly small, dedicated to the load and the secondary voltage higher.

I appreciate any comments.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Jul 22, 2010 6:10 am 
Offline
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 445
Location: Wisconsin
We use the 'standard' IEEE 1584 calculations for 208V systems.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883