mountaineer
|
Post subject: Calculations for 208v System Posted: Thu Jul 22, 2010 5:24 am |
|
Joined: Tue May 18, 2010 7:03 am Posts: 53
|
|
I have read about the exemption for <240V and <125kva transformer. Also have read about the accuracy of each calculation method for different voltage levels. I have come across a situation where the transformer is 225kva, 12kv to 208v for a small pumping station. Which calculation method is most accurate for this? Turns out the 225 kva transformer is large because it feeds a variety of other loads in addition to the substation. The utility has given me a transformer fault current of 28,400A for the secondary side.
Typically the transformers are fairly small, dedicated to the load and the secondary voltage higher.
I appreciate any comments.
|
|
| Top |
|
 |
|
JBD
|
Post subject: Posted: Thu Jul 22, 2010 6:10 am |
|
Joined: Mon Jan 18, 2010 11:35 am Posts: 609 Location: Wisconsin
|
|
We use the 'standard' IEEE 1584 calculations for 208V systems.
|
|