It is currently Fri Sep 25, 2020 12:09 am



Post new topic Reply to topic
Author Message
ekstra   ara
 Post subject: Manufacturers PPE reccomendation with doors closed
PostPosted: Fri Jul 30, 2010 7:28 am 
User avatar

Joined: Thu Sep 24, 2009 5:46 pm
Posts: 25
Square D makes the following recommendation for LV switchgear and MCC's with doors closed: "These components can be operated with the use of PPE 0
under normal circumstances. (See definition of normal
circumstances preceding this table.)"

"Definition of “Normal Circumstances” As used in the table, this term describes equipment that has been:
• properly installed, rated, and maintained;
• properly commissioned and tested after installation;
• in operation, under load, for some period of time."

For safety switches they reccomend:"PPE should be worn per the incident energy level determined at that point in the system"


Comments???


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 1 post ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883