 Post subject: Shock Hazard Analysis
PostPosted: Mon May 12, 2008 12:30 pm 
Offline

Joined: Tue Mar 25, 2008 1:00 pm
Posts: 32
In doing an arc flash analysis, is it necessary to complete a shock hazard analysis and define the different approach boundaries (other than the flash protection boundary)


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon May 12, 2008 1:52 pm 
Offline
Sparks Level

Joined: Mon Apr 14, 2008 7:10 am
Posts: 142
Yes, I provide both for my projects. PTW32 from SKM generator boundaries for Arc flash and shock hazard when you select the template 14 or 18 in custom labels


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon May 12, 2008 3:16 pm 
Offline

Joined: Sun Aug 05, 2007 5:00 pm
Posts: 21
It's not so much that the shock hazard is part of the arc flash study but NFPA 70E requires both a Shock and Flash hazard assesment before live work is done so most people (everyone??) ties them both together and put both on the labels for completeness.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue May 13, 2008 5:35 am 
Offline

Joined: Tue Mar 25, 2008 1:00 pm
Posts: 32
Is the shock hazard information generally taken from the NFPA 70E tables, or calculated with software? I have been using easypower and I see nothing about the shock boundaries in the software.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue May 13, 2008 7:45 am 
Offline

Joined: Sun Aug 05, 2007 5:00 pm
Posts: 21
I believe all the programs have a data base that contains the approach boundary info from NFPA 70E. The labels should reflect what is found in 70E for Limited, Restricted and Prohibited approach limits.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri May 16, 2008 2:00 pm 
Offline
Plasma Level
User avatar

Joined: Wed May 07, 2008 5:00 pm
Posts: 711
Location: Rutland, VT
In EasyPower, when the label are printed both the Flash Hazard and Shock Hazard information is on the label.

For example:

1'-9" Flash hazard boundary
1.9 cal/cm2 flash hazard at 18 inches
#0 PPE level

0.48 kV shock hazard when cover is removed
3'-6" limited approach
1'-0" Restricted approach - Class 00 voltage gloves
0'-1" Prohibited approach - Class 00 voltage gloves

_________________
Barry Donovan, P.E.
www.workplacesafetysolutions.com


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 6 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883