Post subject: Shock Hazard Analysis Posted: Mon May 12, 2008 12:30 pm |
|
Joined: Tue Mar 25, 2008 1:00 pm Posts: 32
|
|
In doing an arc flash analysis, is it necessary to complete a shock hazard analysis and define the different approach boundaries (other than the flash protection boundary)
|
|
| Top |
|
 |
|
Noah
|
Post subject: Posted: Mon May 12, 2008 1:52 pm |
|
Joined: Mon Apr 14, 2008 7:10 am Posts: 142
|
|
Yes, I provide both for my projects. PTW32 from SKM generator boundaries for Arc flash and shock hazard when you select the template 14 or 18 in custom labels
|
|
| Top |
|
 |
|
Catcher13
|
Post subject: Posted: Mon May 12, 2008 3:16 pm |
|
Joined: Sun Aug 05, 2007 5:00 pm Posts: 21
|
|
It's not so much that the shock hazard is part of the arc flash study but NFPA 70E requires both a Shock and Flash hazard assesment before live work is done so most people (everyone??) ties them both together and put both on the labels for completeness.
|
|
| Top |
|
 |
|
deprico
|
Post subject: Posted: Tue May 13, 2008 5:35 am |
|
Joined: Tue Mar 25, 2008 1:00 pm Posts: 32
|
|
Is the shock hazard information generally taken from the NFPA 70E tables, or calculated with software? I have been using easypower and I see nothing about the shock boundaries in the software.
|
|
| Top |
|
 |
|
Catcher13
|
Post subject: Posted: Tue May 13, 2008 7:45 am |
|
Joined: Sun Aug 05, 2007 5:00 pm Posts: 21
|
|
I believe all the programs have a data base that contains the approach boundary info from NFPA 70E. The labels should reflect what is found in 70E for Limited, Restricted and Prohibited approach limits.
|
|
| Top |
|
 |
|
wbd
|
Post subject: Posted: Fri May 16, 2008 2:00 pm |
|
| Plasma Level |
 |
Joined: Wed May 07, 2008 5:00 pm Posts: 881 Location: Rutland, VT
|
|
In EasyPower, when the label are printed both the Flash Hazard and Shock Hazard information is on the label.
For example:
1'-9" Flash hazard boundary 1.9 cal/cm2 flash hazard at 18 inches #0 PPE level
0.48 kV shock hazard when cover is removed 3'-6" limited approach 1'-0" Restricted approach - Class 00 voltage gloves 0'-1" Prohibited approach - Class 00 voltage gloves
_________________ Barry Donovan, P.E. www.workplacesafetysolutions.com
|
|