It is currently Fri Feb 23, 2018 11:24 am



Post new topic Reply to topic
Author Message
ekstra   ara
 Post subject: Soft Starters
PostPosted: Tue Sep 21, 2010 1:00 pm 
Offline

Joined: Sat Nov 21, 2009 3:10 pm
Posts: 25
How do reduced voltage soft starters effect short circuit currents? How are these even modeled in SKM (software I am using)?

Thanks in advance!


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Sep 28, 2010 6:03 am 
Offline
Sparks Level

Joined: Tue May 18, 2010 7:03 am
Posts: 53
I don't use SKM but I was advised to model the soft starts as across the line starters. The reason is that once the motor comes up to speed, typically a contactor closes bypasses the "soft start." It then operates as a typical starter.