 Post subject: Calculating Flash Protection Boundary
PostPosted: Fri Oct 22, 2010 12:29 pm 
Offline

Joined: Thu Jul 09, 2009 11:04 am
Posts: 14
We sometimes have a need to calculate the flash protection boundary for a location with a known incident energy. (I can get into the "why" if needed)

So for example, we would have the following data:

Incident energy
Voltage
Equipment type
Working distance that the known incident energy was calculated based on
(Fault clearing time unavailable)

And we need to calculate the flash protection boundary from the above data.

We have been using an equation derived from IEEE 1584 equations to help us reverse calculate the FPB when the incident energy is already known.

I am attaching the equation and how we derived it below. Has anyone used a similar method? Any feedback?

Thanks.


You do not have the required permissions to view the files attached to this post.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Oct 22, 2010 1:52 pm 
Offline
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
Not following you here, how can you have Ei without knowing the clearing time?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Oct 22, 2010 2:07 pm 
Offline

Joined: Thu Jul 09, 2009 11:04 am
Posts: 14
FCT was known at some point of course to be able to calculate Incident Energy but I don't have it for this calculation.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Oct 25, 2010 5:22 am 
Offline
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
sam314159 wrote:
FCT was known at some point of course to be able to calculate Incident Energy but I don't have it for this calculation.


Sounds like a homework question?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Oct 25, 2010 6:12 am 
Offline
Arc Level

Joined: Wed Jun 04, 2008 9:17 am
Posts: 411
Location: Spartanburg, South Carolina
I don't see anything wrong with your approach. If I follow it correctly, D would be the working distance at which E was calculated.

Have you tried using it on a case where you know the fault clearing time? Calculate both incident energy and the boundary and then use your derived equation to see if it holds.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Oct 25, 2010 7:39 am 
Offline
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 445
Location: Wisconsin
sam314159 wrote:
We sometimes have a need to calculate the flash protection boundary for a location with a known incident energy. (I can get into the "why" if needed).


We do this sometimes, so I have no problem with the concept.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Oct 25, 2010 11:03 am 
Offline

Joined: Thu Jul 09, 2009 11:04 am
Posts: 14
jghrist wrote:
If I follow it correctly, D would be the working distance at which E was calculated.


Exactly right Jghrist.


jghrist wrote:
Have you tried using it on a case where you know the fault clearing time? Calculate both incident energy and the boundary and then use your derived equation to see if it holds.


Yes, I have tried this and the derived equation holds.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Oct 25, 2010 12:39 pm 
Offline

Joined: Thu Jul 09, 2009 11:04 am
Posts: 14
FCT Calculated Both Ways

I attached a side by side calculation of the flash protection boundary using both methods.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Oct 26, 2010 5:25 am 
Offline
Sparks Level

Joined: Tue Feb 24, 2009 7:05 am
Posts: 252
Reverse calculating the FCT may give you a point on the TCC, but it won't give you anything else. If you need another time, because you have another fault current flowing, then you have almost nothing to base yourself on (you only know the TCC may have a decrease in time for an increase in current).

I wouldn't want to trust such a calculation, knowing the original person didn't document it properly. Too much at stake.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Oct 26, 2010 12:46 pm 
Offline
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 445
Location: Wisconsin
Vincent B. wrote:
Reverse calculating the FCT may give you a point on the TCC, but it won't give you anything else.


The OP is not reverse engineering the FCT. They said, given a specific incident energy, they are trying to determine a boundary (distance).


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Oct 26, 2010 1:42 pm 
Offline
Sparks Level

Joined: Tue Feb 24, 2009 7:05 am
Posts: 252
Right, I read a bit too fast the OP.

Doing what's in the 2 pdf, you still assume at least the X factor. Look at the thread about a new configuration for a padmount transformer by Jim Phillips to see that you cannot always assume that the X value is chosen as per the IEEE 1584 table.

Having two unkowns (t and X) makes me feel uncomfortable with any further processing of those values, unless a good sensitivity assessment is made.

I saw a label on a production equipment just yesterday where some info was obviously wrong: Ie = 0.14 cal/cm^2 at 18", HRC 0, AFPB = 43". There's something obviously wrong here. This kind of label makes me wary of assumptions from the results of a calculation, especially if part of the documentation can't be found.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Oct 26, 2010 4:07 pm 
Offline
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 445
Location: Wisconsin
Vincent B. wrote:
Doing what's in the 2 pdf, you still assume at least the X factor. Look at the thread about a new configuration for a padmount transformer by Jim Phillips to see that you cannot always assume that the X value is chosen as per the IEEE 1584 table.


If the X factor cannot be taken from the IEEE table it is not worth making any calculations at all. If the arcing gap corresponds to a table value, then so will the X factor. The problem with the padmount transformer, in the discussion you reference, is the gap is outside of the Table 4 ranges.

Quote:
I saw a label on a production equipment just yesterday where some info was obviously wrong: Ie = 0.14 cal/cm^2 at 18", HRC 0, AFPB = 43". There's something obviously wrong here. This kind of label makes me wary of assumptions from the results of a calculation, especially if part of the documentation can't be found.

Could it be possible the company's policy is to establish a uniform minimum AFB in which case the label would be correct (although I would have thought they would use the 48" distance from NFPA70E)? I know of at least two paper companies that do this.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Oct 27, 2010 10:34 am 
Offline

Joined: Thu Jul 09, 2009 11:04 am
Posts: 14
Vincent B. wrote:

Doing what's in the 2 pdf, you still assume at least the X factor.



This is the OP.

I am 100% of the distance exponent. It is from Table 4.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Oct 27, 2010 6:49 pm 
Offline
Sparks Level

Joined: Tue Feb 24, 2009 7:05 am
Posts: 252
JBD wrote:
Could it be possible the company's policy is to establish a uniform minimum AFB in which case the label would be correct (although I would have thought they would use the 48" distance from NFPA70E)? I know of at least two paper companies that do this.


I don't think so. I'm going back to the same plant on Friday, I'll check other panels. If I cannot find anything satisfying, I'll give a call to the company which did the study (the name is on the label).


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Oct 28, 2010 6:07 am 
Offline

Joined: Thu Jul 09, 2009 11:04 am
Posts: 14
Vincent B. wrote:
Right, I read a bit too fast the OP.

I saw a label on a production equipment just yesterday where some info was obviously wrong:

Ie = 0.14 cal/cm^2 at 18",
HRC 0,
AFPB = 43".

There's something obviously wrong here. This kind of label makes me wary of assumptions from the results of a calculation, especially if part of the documentation can't be found.


Yeah something is obviously messed up here.

0.14 calories @ 18" and 1.2 calories @ 43". I would have expected to see it closer to 5" than 43".


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 15 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883