 Post subject: Ground protection
PostPosted: Mon Dec 06, 2010 12:04 pm 
Offline
Sparks Level

Joined: Mon Apr 14, 2008 7:10 am
Posts: 142
If there is a fault, is it possible that ground fault protection clear the fault first before the overcurrent protection do their due.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Dec 06, 2010 12:38 pm 
Offline
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 445
Location: Wisconsin
Noah wrote:
If there is a fault, is it possible that ground fault protection clear the fault first before the overcurrent protection do their due.


Yes.
In a properly coordinated system we would want a single phase to ground fault to be cleared before it escalates into an arcing line to line fault.

But ground fault relays will usually not operate fast enough to be considered when performing arc flash calculations.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Dec 07, 2010 8:29 am 
Offline
Sparks Level
User avatar

Joined: Tue Oct 26, 2010 5:00 pm
Posts: 115
Location: Maple Valley, WA.
IEEE 1584 has not done AF testing for line to ground faults, only for three phase systems. The AF energy and boundary calculations were derived from three phase testing. Future revisions to the standard will include single phase line to ground faults.

_________________
Robert Fuhr, P.E.; P.Eng.
PowerStudies


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Apr 20, 2011 11:09 am 
Offline

Joined: Tue Apr 12, 2011 6:11 am
Posts: 17
Location: Oregon, USA
Begging the question . . .

Would it be valid for me to assume then, that this means SLG faults and effects are generally NOT included in most arc flash studies at this time ?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Apr 21, 2011 11:11 am 
Offline

Joined: Mon Jan 26, 2009 5:00 pm
Posts: 46
Location: Midwest
I don't have IEEE 1584 in front of me, but I believe they prohibit GF devices and trips to be used in the calculation.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Apr 21, 2011 12:58 pm 
Offline
Arc Level

Joined: Wed Jun 04, 2008 9:17 am
Posts: 411
Location: Spartanburg, South Carolina
Joules Vernier wrote:
Would it be valid for me to assume then, that this means SLG faults and effects are generally NOT included in most arc flash studies at this time ?


Yes. The assumption is that SLG faults will progress into 3P faults and that 3P arcing faults have more energy than SLG arcing faults.

An exception would be electric utilities where the NESC arc flash hazard tables (above 1 kV) were developed assuming SLG faults. This is because of larger phase spacing on OH lines compared to typical industrial enclosed equipment.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Apr 28, 2011 1:32 pm 
Offline

Joined: Tue Apr 12, 2011 6:11 am
Posts: 17
Location: Oregon, USA
My sincere appreciation to each for answers to my SLG related questions. However, this still leads me to a few contingent questions. But since further discussion along this line would be tangential to the origin of this thread, I have posed these questions as the beginning of a new thread. Please see, [url="http://www.arcflashforum.com/showthread.php?p=8148#post8148"]“SLG factors in the arc flash study process ?”[/url]


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 7 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 4 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883