 Post subject: "Need not be considered"
PostPosted: Wed Jun 25, 2008 7:33 am 
Offline

Joined: Mon Sep 24, 2007 7:10 pm
Posts: 16
Location: Washington
I see most interpret this statement the same but there seem to be several schools of thought when it comes to posting the hazard category. The two I am interested in are:

1. Label equipment as PPE #0
2. Label equipment whatever the min required PPE is for the plant (sometimes PPE #2)

What are people doing for equipment that falls in this group? I am referring to the fourth paragraph on page 6 of the 2002 IEEE 1584. any comments are welcome.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Jun 25, 2008 9:18 am 
Offline
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
Just because IEE thinks an arc below this level will not be self sustaining dosent mean there isnt a hazard. How to label this equipment should be discussed with you and your client. I usually recommend using the tables for this equipment.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 3 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883