| Author: | arcflash71 [ Tue May 17, 2011 4:37 pm ] |
| Post subject: | Switchgear Viewing Windows |
Operators in one of our facilities want approval to install viewing windows on 13.8kV switchgear doors to view breaker status (open, closed, test position, etc.). These are a retrofit product from Fluke that have voltage, temperature and pull-out ratings that exceed IEEE C37.20.2 standards for viewing windows. Is this a reasonably safe thing to do with respect to arc flash? Regards |
|
| Author: | wbd [ Wed May 18, 2011 4:21 am ] |
| Post subject: | |
Since the consensus is that credit is not taken for switchgear, MCC, switch doors for reducing AFH, unless specifically designed and rated as arc resistant, I don't think installing the windows will affect the choice of PPE. |
|