ekstra   ara
 Post subject: 1 phase arc flash versus 3 phases
PostPosted: Fri Jul 01, 2011 9:54 am 

Joined: Wed Jun 08, 2011 10:52 am
Posts: 16
for arc flash analysis(3 phases), i upload as arcing short circuit current,

this formula is just for 3 phase or can we use that for single phase equipment as well? if it is applicable then, we need to use single phase current instead of 3 phase current, right? and for system voltage, we need to use phase to ground voltage, right? how about the conductor gap for single phase equipment? and how about the distance factor(D) and distance exponent (x) for single phase equipment?


You do not have the required permissions to view the files attached to this post.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Jul 01, 2011 1:47 pm 
Arc Level

Joined: Wed Jun 04, 2008 9:17 am
Posts: 428
Location: Spartanburg, South Carolina
The formula is from IEEE 1584 and is valid only for 3Ø.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Jul 01, 2011 2:18 pm 

Joined: Wed Jun 08, 2011 10:52 am
Posts: 16
so how do we calculate the PPE, incident energy and arc flash current for single phase?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Jul 01, 2011 2:20 pm 

Joined: Wed Jun 08, 2011 10:52 am
Posts: 16
i though instead of using 3phase bolted current, i would use single phase current in the formula to calculate single phase arc current and instead of using line to line voltage, i would use line to ground voltage for single phase.

i am not sure that would be ok?

any formula avaliable for single phase arc flash?


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883